ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#16420 - 11/11/02 03:34 PM Voltage color I.D.
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
I'm wondering if this is code compliant. I saw a 277 volt lighting application, they used M/C cable and junction boxes in between conduit runs. The proper color as everyone knows for 277V is B.O.Y.. The M/C of course is black, red, white and green. Where the last connection to the fixture were in pipe they installed BOY as phased. Is this allowed, or do you have to have it tagged, or a continuous color? Any replys would be appreciated. TY
Top
Work Gear for Electricians and the Trades
#16421 - 11/11/02 05:07 PM Re: Voltage color I.D.
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
There are no color-code requirements in the NEC as they relate to voltages.

BOY and Bk/R/Bl are not dictated by the NEC, but are often specified by engineers.
_________________________
Peter
Top
#16422 - 11/11/02 05:27 PM Re: Voltage color I.D.
elektrikguy Offline
Member
Registered: 05/25/02
Posts: 132
Loc: woodstock,ga,usa
I wonder why? The Canadian Code does.
Top
#16423 - 11/11/02 05:53 PM Re: Voltage color I.D.
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
i think there's some history here too, just gotta dig up the old timers.....

from my '68 nec...
210-5 Color Code;
(fourth sentence)

All circuit conductors of the same color shall be connected to the same ungrounded feeder conductor throughout the installation.

this also reads in the '71, but the colors dictated in the '68 were arranged into a FPN ( or what appears to be a fpn?)



[This message has been edited by sparky (edited 11-11-2002).]
Top
#16424 - 11/11/02 06:30 PM Re: Voltage color I.D.
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Did I miss something??
"MC is blk, red, white & green, the last connection to the fixture were in pipe, they installed BOY as phased"

Did they use the green for a c.c.c.???
Or did I miss something???
John
_________________________
John
Top
#16425 - 11/11/02 07:13 PM Re: Voltage color I.D.
Wirenuttt Offline
Member
Registered: 11/10/02
Posts: 267
Loc: Massachusetts
Hotline. I'm not sure what you missed.Let me try to clearify. They used 10/3 M/C cable in btween conduit runs. There was conduit leaving the panelboard using Brown, orange yellow to the 1st J.B. from that j.b was 10/3 M/C through the corridors to several j.bs where conduit was branched off to the outlet boxes where the lighting fixtures were attached, and this was brn, org, yellow, phased according to panelboard circuitry, IE: brown being ckt #1 Org being ckt # 3 on so forth. Just the mixing of colors was my concern.
Top
#16426 - 11/11/02 08:06 PM Re: Voltage color I.D.
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
It is most likely that there is a violation of 210.4(D) here. This section requires that where there are two or more voltage systems in a building, that all hots of multiwre branch circuits be identified as to phase and voltage.
Don
_________________________
Don(resqcapt19)
Top
#16427 - 11/12/02 04:43 AM Re: Voltage color I.D.
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Being that 210.4(D) refers to multiwire circuits, I guess a 3 phase motor ckt. at 480V. could be fed with standard MC cable that is colored Bk, R, Bl. and still be in compliance?
Top
#16428 - 11/12/02 05:19 AM Re: Voltage color I.D.
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Don, Rojosy,
Interesting. The term "multiwire branch circuit" wasn't included in 210-4(d) until the '99 NEC. (Which has been adopted at long last here in CA less than 2 weeks ago)
I guess that also means that no feeders must be color coded either, and that a 2 wire circuit can be any color you wish?...S



[This message has been edited by electure (edited 11-12-2002).]
Top
#16429 - 11/12/02 06:15 AM Re: Voltage color I.D.
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
Sparky,

Looking back to the '62 NEC, 210-5 says:
Quote:
Color Code. Where installed in raceways, as aluminum sheathed cable, as open work, or as concealed knob-and-tube work, the conductors of multi-wire branch circuits and two-wire branch circuits connected to the same system shall conform to the following color code. Three-wire circuits - one black, one white, one red; four-wire circuits - one black, one white, one red, one blue; five-wire circuits - one black, one white, one red, one blue, one yellow. Where more than one multi-wire branch circuit is carried through a single raceway the ungrounded conductors of the additional circuit may be of colors other than those specified. All circuit conductors of the same color shall be connected to the same ungrounded feeder conductor throughout the installation.


Abbott's NEC Handbook (Frank Stetka) adds the explanation:
Quote:
The color coding of multi-wire banch-circuit conductors is necessary in order that the loads may be properly balanced between the ungrounded conductors.


Al
_________________________
Al Hildenbrand
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals