The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Search Function
by Webmaster
01/18/17 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 09:17 PM
ESA Arc flash course
by frank
01/18/17 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 29
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
1 registered (Webmaster), 0 Guests and 183 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#163853 - 05/18/07 10:22 PM two wire and GFCI
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
The NEC clearly states that a two wire receptacle can be replaced with a GFCI.
I did that, however, when i test the GFCI with a lightbulb load, hot to ground the GFCI does not trip.

I thought it was a bad GFCI, so i replaced and it still did not trip.

What could be going on?

Thanks.
_________________________
Be kind to your neighbor, he knows where you live


Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#163854 - 05/18/07 10:33 PM Re: two wire and GFCI [Re: Niko]
stamcon Offline
Member

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
There's no "ground" for the current to "leak" to. If you used the test light from the GFCI protected hot, to the ground or grounded conductor of an extension cord, plugged into a grounded receptacle, the GFCI would trip.

steve

Top
#163859 - 05/19/07 06:12 AM Re: two wire and GFCI [Re: stamcon]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
You've got to watch those 2 wire GFI's when they have a metal cover. I stuck a bugeye tester in one and pressed the test button and that energized the faceplate. The GFI passed the trip test as I completed the path to ground because I was touching the faceplate.

Keep in mind that a GFI receptacle is not a cure all for 2 wire replacements. 250-114 has a list of equipment that is required to be grounded and a GFI on a 2 wire circuit doesn't provide the required grounding.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#163860 - 05/19/07 06:46 AM Re: two wire and GFCI [Re: Niko]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Thanks for your input.
i realized what the problem of my test was.

Thanks.
_________________________