#163853 - 05/18/07 10:22 PM two wire and GFCI
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
The NEC clearly states that a two wire receptacle can be replaced with a GFCI.
I did that, however, when i test the GFCI with a lightbulb load, hot to ground the GFCI does not trip.

I thought it was a bad GFCI, so i replaced and it still did not trip.

What could be going on?

Thanks.
_________________________
Be kind to your neighbor, he knows where you live

Top
Work Gear for Electricians and the Trades
#163854 - 05/18/07 10:33 PM Re: two wire and GFCI [Re: Niko]
stamcon Offline
Member
Registered: 03/24/01
Posts: 329
Loc: So San Francisco CA
There's no "ground" for the current to "leak" to. If you used the test light from the GFCI protected hot, to the ground or grounded conductor of an extension cord, plugged into a grounded receptacle, the GFCI would trip.

steve
Top
#163859 - 05/19/07 06:12 AM Re: two wire and GFCI [Re: stamcon]
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
You've got to watch those 2 wire GFI's when they have a metal cover. I stuck a bugeye tester in one and pressed the test button and that energized the faceplate. The GFI passed the trip test as I completed the path to ground because I was touching the faceplate.

Keep in mind that a GFI receptacle is not a cure all for 2 wire replacements. 250-114 has a list of equipment that is required to be grounded and a GFI on a 2 wire circuit doesn't provide the required grounding.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#163860 - 05/19/07 06:46 AM Re: two wire and GFCI [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
Thanks for your input.
i realized what the problem of my test was.

Thanks.
_________________________
Be kind to your neighbor, he knows where you live

Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals