The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 233 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#163834 - 05/18/07 09:27 AM Door swing on utility rooms
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
I just had a discussion with one of our building inspectors regarding the direction a door swings from an electrical room or other utility room. I have an electrical room in a high fault part of the downtown. The door swings into the electrical room and I think that if there was a large energy fault like an arc blast or arc fault where an electricain might be set on fire would present a hazard to the workers. The BI mentioned a worker that drown in a sprinkler room because he could not open the door against the weight of the water.

There does not seem to be a Canadian building code reference that speaks to this. Any other codes address this and how? What about panic hardware? I expect a burning electrician or gas worker might have a problem turning a door knob and pulling the door in in a state of panic. Heck I don't think to many people can remember Stop drop and roll to smother flames.

Top
Building Codes & Related References
#163838 - 05/18/07 11:29 AM Re: Door swing on utility rooms [Re: mikesh]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
NEC has a requirement for panic hardware and 2 doors opening out, but it's only applicable for 1200A and above.
It's 110.26C2.