The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 06:25 AM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 307 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
wirewiz Offline

Registered: 01/27/02
Posts: 123
Loc: WA.
A new customer is opening a new sub shop. Existing Panel is an older FPE panelboard (one of the better ones I have seen) I still recommended they replace it. They are still thinking it over, Think I have them convinced!

Does anyone know of if the bolt-on type breakers are as bad as the stab-loc? Or, are they all garbage?


[This message has been edited by wirewiz (edited 11-11-2002).]

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#16381 - 11/11/02 04:21 AM Re: FEDERAL PACIFIC PANEL QUESTION
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I don't know if the problems associated with FPE apply to bolt-ons, but consider the availabilty & cost of new FPE bolt-ons. How much would it really add to his renovation costs to add a new panel?
Also, double-check the Short-Circuit rating of the old equipment. The utility may have upped the Xfmr at some point since the original pane was installed.

#16382 - 11/11/02 04:57 AM Re: FEDERAL PACIFIC PANEL QUESTION
The Watt Doctor Offline

Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
The biggest problem with FPE, IMHO, is that the breakers don't trip under fault conditions. The price, as Redsy pointed out, is "ungodly". I usually spare no effort in trying to get people to replace their old FPE equipment. If they won't pay me to do it though, I let them live it.

Good Luck,
The Watt Doctor
Altura Cogen
Channelview, TX

#16383 - 11/12/02 06:52 PM Re: FEDERAL PACIFIC PANEL QUESTION
andylea Offline

Registered: 11/12/02
Posts: 29
Loc: ny
i just had a client pay 65 bucks for a federal pacific breaker. why did he buy it, cos his building super told him that that was what his problem was. the real reason, 220v ac line ran in conduit. wire was chaffed or damaged in the pipe, then there was a minor flood, and the federal pacific breaker must have put up one hell of a fight.eventually the wire did what the breaker was sposed to a joke i asked the guy if he noticed any heat in the floor area around the ac unit. he actually replied that his wife had placed her clothes dryer horse there in that particular corner for years. i had to leave the appartment for a few minits........!