The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 11:04 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
0 registered (), 221 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#16376 - 11/10/02 06:13 PM Derating
Wirenuttt Offline

Registered: 11/10/02
Posts: 267
Loc: Massachusetts
I noticed in a foundry that their electric conduits in the ceiling to feed various equipment looked like spegheti. The company would like to run major conduit runs through 2 or 3 large J.B.a spread out all overhead around different areas where you can just pipe up and attach electric equipment hard wired, spliced, and ran through a larger conduit back to the panelboard. There could be a possbility of 10-20 ckts. Does the derating factors of 310-16 apply here, and if so, does this installation warrant???

[This message has been edited by Wirenuttt (edited 11-10-2002).]

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#16377 - 11/11/02 03:25 AM Re: Derating
sparky Offline

Registered: 10/18/00
Posts: 5545
welcome Wirenuttt

IMO, derating would apply, T310.15(B)(2)(a) would dictate 50% off of 310.16 ( 10-20 conductors), however note the math starts at the 90degC collum there.

some consideration for the cieling 'ambient' temp may also apply

The interesting thing is the JB vs. a trough, and the magic '29' conductor limit here;

376.22 Number of Conductors.
The sum of the cross-sectional areas of all contained conductors at any cross section of a wireway shall not exceed 20 percent of the interior cross-sectional area of the wireway. The derating factors in 310.15(B)(2)(a) shall be applied only where the number of current-carrying conductors, including neutral conductors classified as current-carrying under the provisions of 310.15(B)(4), exceeds 30. Conductors for signaling circuits or controller conductors between a motor and its starter and used only for starting duty shall not be considered as current-carrying conductors.