The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
Today at 01:42 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
sparkyinak 8
Potseal 6
Who's Online
2 registered (Webmaster, LongRunner), 227 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#163749 - 05/16/07 07:18 AM Locating Faults In Underground Cables
BubbaJohn Offline
New Member

Registered: 04/03/07
Posts: 3
Loc: South
What method [Or type of equipment] does your company use to "THUMP" your underground cables? We use a Cable Dynamicis/Baur for "Thumping and Radar"
Is there a newer technology for locating the fault in the conductor/cables?

Top
Arc Flash PPE Clothing, LOTO & Insulated Tools
#164144 - 05/26/07 04:16 AM Re: Locating Faults In Underground Cables [Re: BubbaJohn]
RODALCO Offline
Member

Registered: 12/08/05
Posts: 863
Loc: Titirangi, Akld, New Zealand
We use a BAUA surge generator STA 1100 or thumper.
This method is used to locate faults within an armoured cable or for faults between phase to phase and phase to screen.
We use a Biddle stereo microphone, and magnetometer set for pinpointing the fault.
It pays, prior to thumping to mark out the cable route with a Radiodetection or other cable locator. especially in noisy areas.
Accuracy is within one meter of the fault.

For ground faults in single core cables we use the POPIE ( pool of potential in earth ) method.
This is basically a pulsing HV dc supply, which is short circuit proof.
A testcurrent of about 60 mA is enough to pinpoint the fault within 5 cm. (2 inches)
A balanced µA meter with two probes is used for the pinpointing.