The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 137 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#163550 - 05/10/07 07:57 AM Line Voltage Thermostat Calibration
A-Line Offline
Member

Registered: 07/23/04
Posts: 264
Loc: Utah, USA
I recently installed three double pole line voltage thermostats in a customer’s home. The line voltage is 240volts.

The customer says that one of the thermostats reads a temperature of 70 deg. F even though he has it set at 60 deg. F. This thermostat is in a single gang box with two heating elements run to it. The heating elements are imbedded in the ceiling plaster. This is the only thermostat that has two elements run to it. The others have only one element.

I don’t see how controlling the two elements with this thermostat would make any difference on the calibration of the thermostat. From what I can see the thermostat should just monitor the room temperature and open and close the line voltage contacts for the heating elements. The heating elements are wired in parallel with each other. I wouldn’t think you would want them wired in series. Either way I don’t see how this would have any effect on the calibration of the thermostat.

The thermostats are supposed to be factory calibrated with a + or – 2 deg. F accuracy. There are two calibration pots on the thermostat that are sealed with a potting compound.

Does anyone have any experience with the calibration of line voltage thermostats?

Have you ever had to calibrate these in the field?

These are simple manual, non-programmable rotary dial thermostats made by King model HET-2R.

I wouldn’t think calibrating these in the field would be necessary.

I could just try replacing it with another one but was wondering if anyone else has had this problem with line voltage thermostats and what they did to correct it .

I have one sitting here at my desk right now and it’s reading a temperature of 68 deg. F. When I rotate the dial clockwise I can here it click on at about the 68 deg mark and when I rotate it counter clockwise it clicks off at about 62 deg. F. mark.

Maybe the one I installed is just not calibrated properly.

I though I’d see if I could get some input from someone before I go out to look at it.

His daughter told me she thinks he just likes to tinker with things too much and keeps turning the dial up and down and won’t leave it alone.

Any help is much appreciated.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#163555 - 05/10/07 08:33 AM Re: Line Voltage Thermostat Calibration [Re: A-Line]
Ray Offline
New Member

Registered: 05/10/07
Posts: 3
Loc: MA
I would replace it, it could have been knocked around during shipping.

Top
#163556 - 05/10/07 08:36 AM Re: Line Voltage Thermostat Calibration [Re: A-Line]
mhulbert Offline
Member

Registered: 10/19/04
Posts: 133
Loc: Anaheim, CA USA
Maybe the ceiling panels are heating the thermostat hotter/quicker than the air since they are radiant (radiant needs a mass to heat, won't heat the air directly). Also, you need a known good thermometer or temp probe for your meter to see what the room temp really is, then you can go off that. I don't think the cheap little thermometer built into the front of the t-stat cover is a highly accurate instrument. Start with your accurate thermometer, and then see how far off you are. Leave the t-stat alone for at least 6 hours to let the room temp stabilize.

Top
#163558 - 05/10/07 09:32 AM Re: Line Voltage Thermostat Calibration [Re: mhulbert]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
You said "The customer says that one of the thermostats reads a temperature of 70 deg. F even though he has it set at 60 deg. F. This thermostat is in a single gang box with two heating elements run to it. The heating elements are imbedded in the ceiling plaster. This is the only thermostat that has two elements run to it. The others have only one element."
Just for clarity the stat is set at 60 and the temp reading is 70? Is the heat on or off when it is showing 70? If the heat is off then there is no problem unless the stat also controls cooling. If the heat is on and it is 70 degrees in the room there is either a calibration problem or the stat is broke. From your customers statement it appears he thinks the room temperature should be 60 even if it is warmer outside. There can be lots of reasons the room is warmer than the stat setting without there being a problem with the heating. Now if the stat is set at 70 and it is 60 in the room that is a heating problem otherwise he has an AC problem.

Top
#163560 - 05/10/07 12:49 PM Re: Line Voltage Thermostat Calibration [Re: mikesh]
Alan Belson Offline
Member

Registered: 03/23/05
Posts: 1801
Loc: Mayenne N. France
 Quote:
His daughter told me she thinks he just likes to tinker with things too much and keeps turning the dial up and down and won’t leave it alone.


In which case a dollar to a pinch of snuff he's probably had the thing to bits already to see how it works! I have seen these things 'recalibrated' by mispositioning of the dial gear-ring relative to a central pinion.

I've found thermostats to be notoriously inaccurate in controlling actual room temperatures - the vital thing is to have them positioned in the right place. Put the stat in a 'cold spot' in the room and it will always lag the actual temperature.
No need to wait hours for a test, just use a standard thermometer reading, after a few minutes to stabilise, then test the stat by your 'click' test- quite accurate enough to see if it really is 10 deg out.
Since time is money, I'd change it anyway for the one on your desk, he sounds like a fusspot.

Alan
_________________________
Wood work but can't!

Top
#163605 - 05/12/07 03:17 AM Re: Line Voltage Thermostat Calibration [Re: Alan Belson]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I was kind of thinking that somehow the dial may have been "repositioned" in such a way, where the "60°" mark would actually be equal to "70°" ambient temperature, but after seeing the quoted text below, I would say 99.5% chance this is the "Problem"!

 Quote:

His daughter told me she thinks he just likes to tinker with things too much and keeps turning the dial up and down and won’t leave it alone


Line Stats aren't the most accurate things, but they do have at least +/- 5% tolerances with something like a 3° Differential.

As was mentioned before, radiant heat will heat up objects directly, not the enviromental air directly.

This seems to confuse some people with radiant heat strips (ceiling mounted, encased in the Plaster of the "Lid"), as they do not feel warm air immediately.
As a result, they start spinning the Line Stats' dial up and down - eventually calling for a service tech to check things out.

One of the disadvantages to recessed radiant heat strips is when one has to be replaced. The ceiling (Lid) will require patching and texture.
Typical failures come from Toggle Bolts and Lag Screws going through the cable - commonly occurs when someone wants to hang something from the ceiling, encounter "a tough spot" in the plaster, then find out later there is no heat in that room!

Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#163672 - 05/14/07 09:25 AM Re: Line Voltage Thermostat Calibration [Re: Scott35]
A-Line Offline
Member

Registered: 07/23/04
Posts: 264
Loc: Utah, USA
Thanks for the replies.

I ended up calibrating the thermostat.

When I got there it was turning on when I rotated the dial to the 65 deg mark and shutting off when the dial was rotated t the 60 deg mark. The actual temperature was reading 75 deg. I adjusted the calibration using the allen head adjustment pot. It now kicks on at 75 deg. and shuts off at 65 deg.

As I increased the upper set point the span increased as well. There didn’t seem to be any way to decrease the span separately but I think it’s going to work fine. The real test will be next winter when it gets cold again.

I’ll just have to wait and see if he’s happy with it.