#163306 - 05/05/07 08:20 PM Grounding issue
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
went to a family members house to connect a coax cable splitter. When I started removing the connections off the old splitter there was arcing and the lites in the bsmnt. dimmed. After a few minutes they returned to normal. Could this be a result of a loose neutral or improper grounding of service. I am going to run a new ground wire to the water service and install a ground rod. Has anyone ever seen this happen before?
Top
Work Gear for Electricians and the Trades
#163308 - 05/05/07 09:14 PM Re: Grounding issue [Re: sandro2]
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
There is very likely a poor connection somewhere on the service neutral. The cable coax is connected in parallel with the neutral as a result of the code rules. Any arcing accompanied by lights dimming or getting brighter when disconnecting a coax is a very strong indication of a neutral problem. Note that in the case of an open neutral there is also a shock hazard...you could have 120 volts between the two parts of the cable system after you disconnect them.
_________________________
Don(resqcapt19)
Top
#163309 - 05/05/07 10:12 PM Re: Grounding issue [Re: resqcapt19]
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
I have to agree with Don, after hearing my father tell me many tales of this happening...

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals