The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 292 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#163219 - 05/04/07 03:38 AM GFCI Protection on Hot Tub
RonS Offline
New Member

Registered: 05/03/07
Posts: 3
Loc: Charlotte, NC
I went by a prospective customers home yesterday to give an estimate on wiring a hot tub. Upon inspection of the tub the instructions indicate a three wire connection. Two hots and a ground. No neutral connection in the hot tub, no internal GFCI protection provided. There is a neutral generated inside the internal components of the hot tub for lighting and control circuits. Without a neutral connection how would one go about protecting the hot tub with a GFCI breaker. Has anyone run across this before? If I cannot provide the GFCI protection required I will have to tell the customer I cannot do the work.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#163225 - 05/04/07 05:59 AM Re: GFCI Protection on Hot Tub [Re: RonS]
ghost307 Offline

Registered: 05/09/05
Posts: 883
Loc: Chicago Illinois USA
You need to use a 2-pole GFI circuit breaker.
You don't need a neutral to detect ground fault, only a circuit path that can be monitored for any current that isn't accounted for.

12 Amps out on one wire, 12 Amps back on the other...everything's fine.
12 Amps out on one wire, 11.9Amps back on the other...something's wrong with the circuit.