Is anyone here familiar w/ grounding requirements for mobile homes ? Service is o/h to meter to 200a disco to panel. Do I need 2 gnd rods as per stick built? Do I bond the frame (has existing gnd. fr. panel to frame) ?
Top
Work Gear for Electricians and the Trades
#163177 - 05/03/07 08:05 AM Re: Mobile home service [Re: derater]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Define "Mobile Home."

If it's considered as a trailer, then the ground wire to the pedestal is sufficient. Any ground rod will be at the pedestal.

If it's considered "real estate," ... permanently anchored, etc .... then it's ust like a stick-built home as far as the code is concerned.
Top
#163178 - 05/03/07 08:30 AM Re: Mobile home service [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I inspected a bunch of these for the prison system. The typical installation was a service disconnect on a post next to the unit, 4 wire feeder to the panel in the unit and a solid ground electrode conductor from the home panel to the ground under the unit that picked up a lug on the frame along the way. The commercial trailers used as office space always had an 8ga factory installed that bonded the frame. YMMV on residential units.
"Trailers" really come in at least 3 varieties.
There is the travel trailer which is cord and plug connected and stays on wheels
You have the "HUD" approved manufactured home that is basically like a house. The service equipment may actually be in this unit.
You also have a "park model" RV that gets the wheels taken off and sits like a manufactured home but exploits a loophole in the law that allows it to avoid HUD standards. These get connected to a post mounted disconnect. They are hard to get permitted in Florida these days.

I imagine there are variations in between in other places but Florida has made it hard to have anything that won't meet the wind code.

In reality, once you put in all the tie downs the Florida law requires these things are very well "grounded" in any case but we still want to see a rod.
_________________________
Greg Fretwell
Top
#163189 - 05/03/07 12:56 PM Re: Mobile home service [Re: gfretwell]
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
Quote:
They are hard to get permitted in Florida these days.


I wonder why...

Sorry had to say it,
Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top
#163193 - 05/03/07 02:20 PM Re: Mobile home service [Re: derater]
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Mobile home is defined in 550.2, recreational vehicle in 551.2 and park trailer in 552.2. That should cover the 3 types mentioned above.

A mobile home service will need two ground rods and the bonding to the frame should have been installed by the manufacturer. If you're dealing with a used home, you might want to see if the connection is still intact.

Don't forget to comply with 550.32(D). In the area I live in, this means that there must be additional spaces available at the serviceto plug in circuit breakers for loads outside the mobile home.



Edited by Tom (05/03/07 02:22 PM)
Edit Reason: left out info about breaker spaces
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#163211 - 05/03/07 09:34 PM Re: Mobile home service [Re: Tom]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Where the confusion comes in is when this is listed/titled as an "RV" (not HUD compliant) but it looks like a "park model".
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals