#163022 - 04/29/07 08:41 AM GEC and sprinkler system
leespark Offline
Member
Registered: 01/17/04
Posts: 54
Loc: Massachusetts
How should I handle the grounding electrode system for a 400 amp service?

I plan on installing a 1/0 copper from the main disconnect to the within 5' of where the water service enters the building and jump the water meter unspliced. I am also installing a #6 from the main disconnect to 2 ground rods spaced at least 6' apart.

However, this building has a separate incoming water service for the sprinkler system. Can I install a bonding jumper sized according to 250.66 (1/0) from the sprinkler service to the water service and connect it to the GEC using a split bolt? Or should this conductor also be run back to the main disconnect? I'm a little confused by 250.70 which I beleive is referring to my situation.

Thanks
Top
2017 / 2014 NEC & Related Books and Study Guides
#163024 - 04/29/07 08:53 AM Re: GEC and sprinkler system [Re: leespark]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
There are different ways of doing this and complying with the Code.
1. From the sprinkler system (within 5 foot of entry*) take the wire to the service.
2. From the sprinkler (within...*) take the wire to the GEC and use an irreversable crimp, not a split bolt.
3. From the sprinkler take the wire to the water pipe and use a pipe clamp.
4. If you have building steel go from the service to the steel. Then you can take the water to the steel and the sprinkler to the steel.
The last method saves alot of copper.
Alan--

_________________________
Alan--
If it was easy, anyone could do it.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals