#162912 - 04/27/07 02:13 PM Single Phase 220V from 3 phase Y 208
GCI Offline
New Member
Registered: 04/26/07
Posts: 1
Loc: AZ, USA
I have 3 phase Y 208 at my office. Purchased a lift that has a pump motor on it that requires 220 sigle phase. Any two legs of three phase are 120 degrees out of phase, I have seen wiring for welders wired this way, but a - motor probably requires 180 degrees phase difference? Step up transformer or other solution?
Top
Work Gear for Electricians and the Trades
#162921 - 04/27/07 03:51 PM Re: Single Phase 220V from 3 phase Y 208 [Re: GCI]
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
Just hook it up to 208V. It will work fine.

What type of engineer are you?
Top
#162937 - 04/27/07 05:13 PM Re: Single Phase 220V from 3 phase Y 208 [Re: GCI]
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Originally Posted By GCI
I have 3 phase Y 208 at my office. Purchased a lift that has a pump motor on it that requires 220 sigle phase. Any two legs of three phase are 120 degrees out of phase, I have seen wiring for welders wired this way, but a - motor probably requires 180 degrees phase difference? Step up transformer or other solution?


2-wire motors are wired line-line. There is no phase difference between only two wires. The concern is that you actually have enough voltage to run your motor, the worst case is you will need to use a buck-boost transformer. Is your motor really 220V and not 230V?
Top
#163009 - 04/28/07 08:01 PM Re: Single Phase 220V from 3 phase Y 208 [Re: JBD]
Dave T Offline
Member
Registered: 01/22/05
Posts: 155
Loc: Waukesha, WI, USA
Have you asked the manufacturer or the pump motor manufacturer??
This is not to be taken for an answer to you application but some background for the answer you should get from the manufacture.
If in fact it is a 220v motor od it NEMA rated? If so antivipate that it is able to operate satisfactory a +-10% of that which would be 220 x.90=198v. I did not say that the device was capable to operate at down to 198v but there's a good chance that it would be an accurate answer.
Remember one thing. If a motor is rated at 10HP at 220v it will draw a specific amount of amps to product 10HP. In doing so there will be losses in heat. Now reduce that voltage to 198v. To produce the same 10HP the motor would have to draw more amps to produce that same 10HP. More amps = more heating.
It is common that whem a motor is applied it never is required to produce its nameplate HP anyway.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals