#162825 - 04/25/07 08:39 PM Need some Help with fuel pumps
RDK Offline
Member
Registered: 04/07/07
Posts: 33
Loc: Lac LA Biche
I have a few questions. I have a company that has three fuel pumps. The pumps are the simple type nothing fancy. The owner wants when the pumps run a light on the shop flashes to let the works know when the pumps are running.Now there is always power at the pumps and installing relays wont work because the light would always be on.So what do I have for options?
Top
Work Gear for Electricians and the Trades
#162838 - 04/26/07 01:05 AM Re: Need some Help with fuel pumps [Re: RDK]
skipr Offline
Member
Registered: 01/03/05
Posts: 39
Loc: Huntington Beach, Ca.
If there is always power at the pumps, do you mean they are always running? I would assume that is not the case. I would think there is a control to a mag starter.
Top
#162842 - 04/26/07 03:41 AM Re: Need some Help with fuel pumps [Re: RDK]
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
There might be power at the pump all the time but the motor isn't running all the time. What brand pump are they?? Are they old style mechanical pumps?? Most have several unused switches in reset mechanism that could be used to turn on a light.
Top
#162849 - 04/26/07 04:52 AM Re: Need some Help with fuel pumps [Re: walrus]
RDK Offline
Member
Registered: 04/07/07
Posts: 33
Loc: Lac LA Biche
They are older style pumps ill try to get pix
Top
#162869 - 04/26/07 11:49 AM Re: Need some Help with fuel pumps [Re: RDK]
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
Why not install current-activated relays on the circuits to the pumps, and use them to turn on lights or whatever?

Something like these:

http://www.ssac.com/catalog/ECS01A01.pdf

With these, you can do all your wiring back in the shop, and not need to bring additional wires back from the pumps (avoiding the hazardous location sealing issues).


Edited by NJwirenut (04/26/07 11:52 AM)
Top
#162879 - 04/26/07 02:29 PM Re: Need some Help with fuel pumps [Re: NJwirenut]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I didn't see a price on that relay.
_________________________
Greg Fretwell
Top
#162880 - 04/26/07 02:41 PM Re: Need some Help with fuel pumps [Re: gfretwell]
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
I've bought the SSAC units for around $150 or so. There are somewhat cheaper options, as well:

http://web1.automationdirect.com/adc/Overview/Catalog/Sensors_-z-_Encoders/Current_Sensing_Switches
Top
#162883 - 04/26/07 03:14 PM Re: Need some Help with fuel pumps [Re: NJwirenut]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
Talk about not enough information! All of my bus garage installations show when the selected lead and lag pumps are running. If I didn't have it already, I could cheat using my Veeder-Root Tank Monitoring System. It wouldn't show that a pump is running BUT I could program each tank's "Sudden Loss Alarm" to a ridiculously low number of gallons. That would show when you were actually dispensing fuel. If the annoying beep and red lamp or LED weren't enough, a relay output could be programmed to alarm for sudden loss in any tank. I only offer this up because most folks aren't issued green stickers, allowing them to receive fuel deliveries, unless they already have this capability.

All of the Gasboy dispensers that I deal with control tank mounted STPs. The drive for their contactor comes from the reset counter. In other words, you throw the lever, the counter zeros, and the contacts close on the next click that you hear. There are also contacts for slow and fast fuel solenoids. I believe that there is often an additional dry contact available. Of course, all this stuff is at the pumps and no fun if sufficient spares weren't pulled. And boy do I HATE CHOPPIN' AWAY AT CHICO!!! That's why I would look into your TMS for the Sudden Loss settings.
Joe
Top
#162914 - 04/27/07 02:28 PM Re: Need some Help with fuel pumps [Re: JoeTestingEngr]
walrus Offline
Member
Registered: 07/25/02
Posts: 680
Loc: Bangor Me. USA
Originally Posted By JoeTestingEngr
I could cheat using my Veeder-Root Tank Monitoring System. It wouldn't show that a pump is running BUT I could program each tank's "Sudden Loss Alarm" to a ridiculously low number of gallons. That would show when you were actually dispensing fuel. If the annoying beep and red lamp or LED weren't enough, a relay output could be programmed to alarm for sudden loss in any tank. I only offer this up because most folks aren't issued green stickers, allowing them to receive fuel deliveries, unless they already have this capability.
I can assure you that many places sell fuel without having a TLS350. But that is a good idea if it was available.

Top
#162917 - 04/27/07 03:01 PM Re: Need some Help with fuel pumps [Re: walrus]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
Originally Posted By walrus
Originally Posted By JoeTestingEngr
I could cheat using my Veeder-Root Tank Monitoring System. It wouldn't show that a pump is running BUT I could program each tank's "Sudden Loss Alarm" to a ridiculously low number of gallons. That would show when you were actually dispensing fuel. If the annoying beep and red lamp or LED weren't enough, a relay output could be programmed to alarm for sudden loss in any tank. I only offer this up because most folks aren't issued green stickers, allowing them to receive fuel deliveries, unless they already have this capability.
I can assure you that many places sell fuel without having a TLS350. But that is a good idea if it was available.



The city environmental folks that I deal with are getting more and more demanding all the time. They want us to be able to produce the results of our .2 gallon per hour leak tests on request. They even want 3rd party annual testing of our manway floats. We still have alot of Pneumercator stuff that we are upgrading to V-R These guys keep telling me that everyone has to comply to get their sticker so I would think anyplace that can do mandatory leak testing could trigger on sudden loss.
Joe
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals