The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 101 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#162145 - 04/13/07 04:50 PM Crimp vs. Setscrew - 500 MCM CU
Grover Offline
Member

Registered: 01/19/05
Posts: 110
Loc: Sebago, ME, USA
Opinions? Experiences? Old school boss wants setscrew terminations - I favor proper die hydraulic crimp. Application is parallel runs - 1200 A 480 3 phase. Total of 64 terminations.

Square D QED Switchboard provides setscrew lugs for 32 of the terminations - what do do with the rest?

Appreciate input.

Grov

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#162153 - 04/13/07 06:28 PM Re: Crimp vs. Setscrew - 500 MCM CU [Re: Grover]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Grov:
4 conductors per phase??
or ???
64 terminations; I'm assuming switchboard to padmount xfr? At 4 per phase...16 and 16..

I'm confused. I'm 'old school' too (59), but I'm partial to crimp terminations.

I've done setscrew lugs (factory installed in gear) and crimps at the padmount supplied by me, installed by me. Our utility requires EC's to do secondary terminations at padmounts.

John
_________________________
John

Top
#162162 - 04/13/07 08:04 PM Re: Crimp vs. Setscrew - 500 MCM CU [Re: HotLine1]
Grover Offline
Member

Registered: 01/19/05
Posts: 110
Loc: Sebago, ME, USA
Hotline - sorry to confuse....

4 pipes - A,B,C,N in each - parallel.

Genset ->Switchgear, Switchgear to MCC

Switchgear has setscrew lugs supplied - Square D QED.

My old school guy has apparetly had trouble with failed crimps (wrong die, not enough pressure?). QED ame with setscrew lugs - weakens my arguement.

I've always used crimps with no complaints...

Grov

Top
#162170 - 04/13/07 10:38 PM Re: Crimp vs. Setscrew - 500 MCM CU [Re: Grover]
ITO Offline
Member

Registered: 11/26/06
Posts: 341
Loc: Texas
What do the specs say, and what type of terminations did you submit on?
_________________________
101┬░ Rx = + /_\

Top
#162192 - 04/14/07 10:38 AM Re: Crimp vs. Setscrew - 500 MCM CU [Re: ITO]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
I will normally toss out the manufacture provided set screw connectors and replace them with compression connectors on equipment of that size. We always use a dieless hydraulic crimper so there is no problem with the wrong die or incorrect pressure. For that many terminations I would be using the cordless hydraulic crimper in place of the hand pumped one.
Don
_________________________
Don(resqcapt19)

Top
#162199 - 04/14/07 11:05 AM Re: Crimp vs. Setscrew - 500 MCM CU [Re: resqcapt19]
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Odds are that the manufacturer makes lugs for the purpose. I've seen 6 and 8 hole lugs like that, and four hole are pretty common. If you dig through the SqD catolog I'll bet you find them. Properly torqued they are just as good a connection IMO.

If you crimped them all - what would you be doing for all the connections to the busswork? Does it have bolt patterns for that? Dont 500MCM crimps have 2-bolts per?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#162211 - 04/14/07 02:42 PM Re: Crimp vs. Setscrew - 500 MCM CU [Re: e57]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Mark,
Crimps are made in either single or two hole type. Many of the larger mechanical lugs are two hole with the same pattern as the crimps.
 Quote:
Properly torqued they are just as good a connection IMO.

In my opinion a properly installed mechanical lug is never as good as a properly installed compression lug. Both will do the job, however I believe that the compression are better. The contact pressure on the mechanical lug is not as high and the quality of the installation is more dependent upon the skill of the installer as compared to installing a compression lug with a dieless hydraulic crimp tool. If you cut through the connector and the wire on a compression termination that was installed with a hydraulic crimp tool, it is hard to tell that the wire was stranded. I guess maybe my preference comes from working mostly on industrial projects when crimp connections are often part of the job specifications.
_________________________
Don(resqcapt19)

Top