#162141 - 04/13/07 03:22 PM Residential 2 apartment load calcs.
fredc Offline
Junior Member
Registered: 11/09/06
Posts: 1
Loc: freehold NJ
Hey I was wondering if someone could help me figure out what size wire I need to use. It is a 2 family house has 2 sub panels 200amps each. I am putting a 2 gang stackable meter pan. I am use to single family house where everything is straight forward. The problem is these apartments are small only 900sf each. The 200 amp panels are an over kill. Could someone help me out here?
Top
Work Gear for Electricians and the Trades
#162151 - 04/13/07 06:12 PM Re: Residential 2 apartment load calcs. [Re: fredc]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You have to serve 200a if that is the breaker you have. 4/0 al to each and 600kcmil (or parallel 4/0) to the service point, the way I see it. The PoCo will probably connect that to a 2ga al triplex drop.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals