The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#161994 - 04/11/07 09:58 AM Communications
RSmike Offline
Member

Registered: 11/27/02
Posts: 130
Loc: Holland, MI USA
Is running a shielded twisted pair communications cable (CAN-bus operating at 5-24vdc) along with a SO cord 18/3 (operating at 3A - 120VAC) inside the same liquid tight flexible nonmetallic conduit (LFNC) a legal installation with respect to NPFA70-2005? With respect to NPFA79-2007?

Put on your thinking caps gentlemen,

RSLater,
RSmike

Top
2014 / 2011 NEC & Related Books and Study Guides
#162001 - 04/11/07 03:05 PM Re: Communications [Re: RSmike]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
SO Cord can not be installed in a raceway.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#162011 - 04/11/07 05:05 PM Re: Communications [Re: iwire]
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
Unless all conductors, not cables, are rated for the maximum voltage in use within the raceway, then this type of installation isn't permitted. My question would be how these circuits are separated at the ends of the liquid-tight since any approved enclosure would have separate high and low-voltage compartments?

I'd go with the shielded communications cable routed outside of the liquid-tight and run THHN, etc. inside.
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#162012 - 04/11/07 05:14 PM Re: Communications [Re: EV607797]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
 Originally Posted By: EV607797
My question would be how these circuits are separated at the ends of the liquid-tight since any approved enclosure would have separate high and low-voltage compartments?


There are many industrial enclosures which contain PLCs and/or drives that use CANBUS for communications that do not have separated LV compartments.

This sounds like a Class 1 or Class 2 application although <24V communications circuits are not always "power limited".


Edited by JBD (04/11/07 05:17 PM)

Top
#162021 - 04/11/07 07:55 PM Re: Communications [Re: JBD]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Communications wiring and Power wiring are not permitted in the same raceway I don't care what the insulation ratings are. Article 800 Section 800.133 NFPA70 2005 Edition.
_________________________
George Little

Top
#162032 - 04/12/07 06:37 AM Re: Communications [Re: George Little]
RSmike Offline
Member

Registered: 11/27/02
Posts: 130
Loc: Holland, MI USA
Unless I missed it I also don't see NPFA70 allowing this or it's not specifically stated.

However, I read NPFA79 13.1.3 as allowing this; comments?

RSLater,
RSmike

Top
#162033 - 04/12/07 07:10 AM Re: Communications [Re: George Little]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
 Originally Posted By: George Little
Communications wiring and Power wiring are not permitted in the same raceway I don't care what the insulation ratings are. Article 800 Section 800.133 NFPA70 2005 Edition.


Here we go with terminology.

CAN bus is normally used for interconnecting automation devices which is is probably a 725 remote-control and signalling application. 725.55(D) and 725.55(E) have provisions for mixing Class 2 and Class 3 circuits with other wiring.

Article 800 is for "central station systems" like telephones. However, 830 address networks so 830.133(A)(1)(d) Excpt #1 may be applicable.

Top
#162038 - 04/12/07 08:11 AM Re: Communications [Re: JBD]
RSmike Offline
Member

Registered: 11/27/02
Posts: 130
Loc: Holland, MI USA
725.55(D)(2)a - makes me a happy person.

What about SO cord in LFNC? Why is this not allowed? It terminates so well into the operator interface terminal device I'm powering. THHN is cheaper so I'll probably do that.

RSthanks,
RSmike

Top
#162047 - 04/12/07 09:58 AM Re: Communications [Re: RSmike]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
George isn't class 1 OK in the raceway with the circuit(s) it controls?
I agree class 2/3 is not.
I suppose the real question is whether CanBus is a class 1 compliant wiring method
_________________________
Greg Fretwell

Top
#162058 - 04/12/07 12:09 PM Re: Communications [Re: gfretwell]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Greg- The original post only said Communication cable which put me in Article 800. I don't really know what CanBus is and maybe you are correct. Don't sound to me like 725 is even involved. Maybe I don't know what I'm talking about. The Scope of 800 is Communication Circuits and so that's where I went. Straighten this old man out \:\)