#161967 - 04/10/07 10:21 PM ? for resi inspectors  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
Does changing the breaker constitute " working on the circuit" ? i.e. does a panel change (only) require AFCI's for bedrooms ?


Work Gear for Electricians and the Trades

#161971 - 04/10/07 11:25 PM Re: ? for resi inspectors [Re: derater]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
That is going to be a local call at plan review time.


Greg Fretwell

#162028 - 04/12/07 07:15 AM Re: ? for resi inspectors [Re: gfretwell]  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
Gfretwell; way past planning. the ? relates to a legal matter. IS it code or not ?


#162029 - 04/12/07 07:44 AM Re: ? for resi inspectors [Re: derater]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,803
Brick, NJ USA
Derater:
In NJ, this may be classified as a 'repair' and not require a permit or insp.
NJ does not require AFCI protection, as it was amended in the UCC.
Probably a local/area clarification.
Where are you??
John


John

#162036 - 04/12/07 10:26 AM Re: ? for resi inspectors [Re: HotLine1]  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
I'm in Cent Pa. A 'home inspector' is contending that changing out the panel requires installing AFCI's. I've never heard of such a thing.


#162039 - 04/12/07 11:32 AM Re: ? for resi inspectors [Re: derater]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 781
Winchester, NH, US
What was there previously, breakers or fuses? Were any circuits added?


#162040 - 04/12/07 11:41 AM Re: ? for resi inspectors [Re: derater]  
macmikeman  Offline
Member
Joined: Jul 2002
Posts: 717
Honolulu, Hawaii
Originally Posted by derater
I'm in Cent Pa. A 'home inspector' is contending that changing out the panel requires installing AFCI's. I've never heard of such a thing.


The 2005 code requires AFCI protection of the branch circuit supplying all 120 volt 15 and 20 amp outlets INSTALLED in bedrooms of dwellings. A simple panel replacement usually does not involve any installation of new 120 volt outlets in bedrooms of dwellings, so therefore a careful read of the code section requiring afci protection will highlight the fact that "home inspectors" are generally as far off as my spelling seems to always be.


#162043 - 04/12/07 12:43 PM Re: ? for resi inspectors [Re: macmikeman]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
I assume it is universal but any permit pulled in Lee County Florida will go through plan review. It may just be a rubber stamp but it can also be kicked back if it does not include the things they require. That is where the decision would be made if a panel upgrade triggers AFCI installation.
Of course if this gets done without a permit I am not sure who would be there to tell you AFCIs would be required. It is certainly not going to be a home inspector. They are not legally able to cite code unless they are licensed CODE inspectors. Florida does not even recognize "home inspector" as a regulated industry and their "inspectors" are just informal advisors with an occupational license. A home inspector can advise a client of anything they want, down to their favorite color for the toilet but it has no force of law.


Greg Fretwell

#162044 - 04/12/07 12:46 PM Re: ? for resi inspectors [Re: gfretwell]  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,060
Estero,Fl,usa
BTW if you want a laugh, go over the the NACHI BB and see the ridiculous things working home inspectors think are "code".
http://www.nachi.org/forum/forumdisplay.php?f=19


Greg Fretwell

#162048 - 04/12/07 01:15 PM Re: ? for resi inspectors [Re: gfretwell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,803
Brick, NJ USA
Greg:
Yes, we 'review' each app, but plans are not required for 'minor' work (EC's)

"Home Inspectors" can only 'suggest', not require anything here. Most, if not all 'suggest' that a Lic Professional be consulted (CYA on that)

John


John

Page 1 of 2 1 2

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 208
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.023s Queries: 16 (0.004s) Memory: 0.8168 MB (Peak: 0.9983 MB) Zlib enabled. Server Time: 2017-03-29 01:15:34 UTC