The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 122 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#161678 - 04/06/07 11:18 AM Fire Alarm T Tap
CRM Offline
Member

Registered: 02/29/04
Posts: 73
Loc: Alberta Canada
I've got an edwards QS4 fire alarm, I've got an adressible loop going around the building, 2 wires leaving and 2 wires returning. Can I tap 2 wires off the loop at any point to feed an adressible pull station, but not run 2 wires back onto the loop. Thanks for any input.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#161710 - 04/06/07 06:21 PM Re: Fire Alarm T Tap [Re: CRM]
Steve Miller Offline
Member

Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
The 2 back are what create the Class A system. To the best of my knowledge, no you can't. You need the 2 going back. If the 2 going out get broken the Class A will still function because it is "double end fed".

Top
#161734 - 04/07/07 04:46 AM Re: Fire Alarm T Tap [Re: Steve Miller]
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Depending on how far you need the circuit extension, and the size room the device is in, the NFPA 72 (FA Code) would allow you to take two cables (2 wires in each plus shield) and run to the new device. This would effectively give you the two there and the two back.

You have some limitations in this scheme if they are in the same raceway or bundle because there would need to be some separation if the area served was large.
_________________________
Ron

Top
#161738 - 04/07/07 05:38 AM Re: Fire Alarm T Tap [Re: Ron]
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
I have limited knowledge of addressable fire alarm systems. My question is aren't two wire class B system initiating device circuits more popular than the class A system? What are the advantages of the class A system?


Edited by Frank Cinker (04/07/07 05:41 AM)
Edit Reason: typo

Top
#161742 - 04/07/07 07:00 AM Re: Fire Alarm T Tap [Re: Frank Cinker]
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Class A is generally not code required, but offers better reliability during certain faults and open circuit conditions.
_________________________
Ron

Top
#161744 - 04/07/07 07:38 AM Re: Fire Alarm T Tap [Re: Ron]
yanici Offline
Member

Registered: 09/03/06
Posts: 57
Loc: Atlantis
Why not just identify your"in" and "out" pairs and then run 2 pair to the new pull station. Then splice them accordingly at the junction.

Top
#161748 - 04/07/07 08:10 AM Re: Fire Alarm T Tap [Re: yanici]
deverson Offline
Member

Registered: 03/07/05
Posts: 20
Loc: Mosinee, WI USA
T-taps are allowed on Simplex addressable systems. I'm not sure if there is a maximum number of T-taps per Mapnet zone. If you remove a head or a base you do get notification of that trouble. T-tapping is a nice feature for the troubleshooter because when you have to remove a base for replacement you don't end up with up to 256 missing heads. These are initiating circuits and NOT signal circuits. I've had lots of experience on 4100, 4100U panels and on hardwired in lots of buildings, installation and repair.
Dave

Top
#161830 - 04/08/07 01:31 AM Re: Fire Alarm T Tap [Re: deverson]
sparkydudeuk Offline
Junior Member

Registered: 07/11/05
Posts: 8
Loc: burton upon trent ,staffordshi...
Over here in the Uk where we use addressable alarm systems, we are only permitted to take t taps off a system if it is wired in a four core and ground cable. You are not permitted to use a 2 core cable as it will not provide the recommended monitoring and re feeding of the loop if there is a fault and the isolators operate. With the systems we use, you can get an interface which you put on the loop and then wire a conventional zone with 2 cores to you r chosen area, and then it is monitored via the interface.

Nick

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals