The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 297 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#161631 - 04/05/07 02:34 PM outdoor gas/diesal tank installation
johnd24 Offline

Registered: 07/11/01
Posts: 66
Anyone have a drawing for a outdoor fuel tank at a school for their buses.
I installed a shunt trip an e-stop button but unsure how far the e-stop can be from the tank.Also installed rigid pipe with expliosion proof fittings and sealoffs.

2014 / 2011 NEC & Related Books and Study Guides
#161641 - 04/05/07 05:39 PM Re: outdoor gas/diesal tank installation [Re: johnd24]
ausador Offline

Registered: 03/26/07
Posts: 49
Loc: Central Florida
The Emergency pump shutdown is to be locacated at least 20 feet but less than 100 feet from the dispenseing location. Look at article 514 for more info.

#161645 - 04/05/07 07:16 PM Re: outdoor gas/diesal tank installation [Re: ausador]
JoeTestingEngr Offline

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
I don't know the minimum requirement but that's one thing we don't skimp on. We put them just about anywhere you'll pass on the way out of a problem in the fueling islands and a couple of distant points that you can view them from. We also have a connection to the FACP so that any zone associated with or nearby the fueling will cause an E-Stop on alarm. We can bypass the FACP E-Stop but that will put the FACP into Trouble or Supervisory until enabled. We only use one key reset switch in the Foreman's offices. I sometimes find these reset switches jumpered at which time I tend to light a little fire of my own.

#161666 - 04/06/07 05:52 AM Re: outdoor gas/diesal tank installation [Re: johnd24]
walrus Offline

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
If your trying to meet NEC a shunt trip won't cut it. Doesn't shut off grounded conductor. Is it an unattended operation??