The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#161554 - 04/04/07 06:46 AM Romex and Extension Cords
BubbaJohn Offline
New Member

Registered: 04/03/07
Posts: 3
Loc: South
I see many electrical safety tips that caution against using Romex wire for extension cords, but never the reason. I'm guessing the reason is that the insulation is not durable to fit the grade, right? If not what is the reason? What type of insulation should an "approved" extension cord be constructed from? many thanks

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#161557 - 04/04/07 08:06 AM Re: Romex and Extension Cords [Re: BubbaJohn]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
The short answer is in the name. Extension cords should be made from "cord", not cable.
Since this is usually "hard service" it should be some kind of hard service cord.
Most OSHA inspectors have trouble with any field built extension cords anyway. If you do make one, be sure you have all listed parts, used in the way they are listed (no handy boxes with a Romex connector)
Greg Fretwell

#161561 - 04/04/07 08:27 AM Re: Romex and Extension Cords [Re: gfretwell]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
At one time, I was employed to do some tests on sundry connectors that were intended to be used with cords. One of the test was to hang a weight from the cord, to see if the connector did actually prevent the strain from being transmitted to where the wires were connected.

I did test several such connectors on Romex, rather than 'extension cord' material. In every instance, the connector failed to hold on to the romex well enough. That is, the outer jacket would work free of the connector, and you'd be left with the wires holding the weight.

#161564 - 04/04/07 08:51 AM Re: Romex and Extension Cords [Re: renosteinke]
mikesh Offline

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Another consideration is the romex has solid conductors and they are not especialy suited to frequent flexing. The jackets certainly are not meant for rough duty either.

#161571 - 04/04/07 12:03 PM Re: Romex and Extension Cords [Re: renosteinke]
macmikeman Offline

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
I think that is much the same reason OSHA frowns upon the cord end replacement caps you can put on. After a while of use, they tend to work themselves loose from the cord sheath and expose conductors also.

#161575 - 04/04/07 12:35 PM Re: Romex and Extension Cords [Re: macmikeman]
George Offline

Registered: 02/23/02
Posts: 380
It is common to run NM for long temp extension cords where the ends are not moved frequently.

The only reason that NM is not approved for extension cords is that is is not tested for that purpose.

#161581 - 04/04/07 01:50 PM Re: Romex and Extension Cords [Re: George]
Ann Brush Offline

Registered: 12/27/05
Posts: 155
Loc: Ohia
On the cord vs cable naming issue: I recently used Bus Drop CABLE for a heavy duty "extension cord" from a PTO generator to my house - the setup had a interlocked breaker installed in the main panel and the whole shebang was passed by the ahj. My point: Bus drop CABLE was ok to plug and cord connect the PTO generator to the house. BTW I agree with the comments on strain releif using NM.

#161740 - 04/07/07 06:24 AM Re: Romex and Extension Cords [Re: Ann Brush]
Texas_Ranger Offline

Registered: 12/17/01
Posts: 2332
Loc: Vienna, Austria
That one's a classic... I just took two extension cords made with German NYM out of service at the local church.

#161756 - 04/07/07 10:08 AM Re: Romex and Extension Cords [Re: BubbaJohn]
Elviscat Offline

Registered: 08/13/05
Posts: 214
Loc: Seattle Washington USA
I'd say it's the shape and flexability issues i.e. it pulls out of connectors too easily and is pretty useless as an extention cord because it's too inflexible, plus I doubt that the solid wire has as high a pull-out force from the connector itself, though this is just conjecture. I think that the romex jacket durability v.s. extention cord durability is a fairly minor issue.


#161766 - 04/07/07 12:23 PM Re: Romex and Extension Cords [Re: Elviscat]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
This is one my wife took away from a trade ... wait for it ...

Greg Fretwell

Page 1 of 2 1 2 >

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals