#161554 - 04/04/07 06:46 AM Romex and Extension Cords
BubbaJohn Offline
New Member
Registered: 04/03/07
Posts: 3
Loc: South
I see many electrical safety tips that caution against using Romex wire for extension cords, but never the reason. I'm guessing the reason is that the insulation is not durable to fit the grade, right? If not what is the reason? What type of insulation should an "approved" extension cord be constructed from? many thanks
Top
Work Gear for Electricians and the Trades
#161557 - 04/04/07 08:06 AM Re: Romex and Extension Cords [Re: BubbaJohn]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The short answer is in the name. Extension cords should be made from "cord", not cable.
Since this is usually "hard service" it should be some kind of hard service cord.
Most OSHA inspectors have trouble with any field built extension cords anyway. If you do make one, be sure you have all listed parts, used in the way they are listed (no handy boxes with a Romex connector)
_________________________
Greg Fretwell
Top
#161561 - 04/04/07 08:27 AM Re: Romex and Extension Cords [Re: gfretwell]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
At one time, I was employed to do some tests on sundry connectors that were intended to be used with cords. One of the test was to hang a weight from the cord, to see if the connector did actually prevent the strain from being transmitted to where the wires were connected.

I did test several such connectors on Romex, rather than 'extension cord' material. In every instance, the connector failed to hold on to the romex well enough. That is, the outer jacket would work free of the connector, and you'd be left with the wires holding the weight.
Top
#161564 - 04/04/07 08:51 AM Re: Romex and Extension Cords [Re: renosteinke]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Another consideration is the romex has solid conductors and they are not especialy suited to frequent flexing. The jackets certainly are not meant for rough duty either.
Top
#161571 - 04/04/07 12:03 PM Re: Romex and Extension Cords [Re: renosteinke]
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
I think that is much the same reason OSHA frowns upon the cord end replacement caps you can put on. After a while of use, they tend to work themselves loose from the cord sheath and expose conductors also.
Top
#161575 - 04/04/07 12:35 PM Re: Romex and Extension Cords [Re: macmikeman]
George Offline
Member
Registered: 02/23/02
Posts: 375
It is common to run NM for long temp extension cords where the ends are not moved frequently.

The only reason that NM is not approved for extension cords is that is is not tested for that purpose.
Top
#161581 - 04/04/07 01:50 PM Re: Romex and Extension Cords [Re: George]
Ann Brush Offline
Member
Registered: 12/27/05
Posts: 152
Loc: Ohia
On the cord vs cable naming issue: I recently used Bus Drop CABLE for a heavy duty "extension cord" from a PTO generator to my house - the setup had a interlocked breaker installed in the main panel and the whole shebang was passed by the ahj. My point: Bus drop CABLE was ok to plug and cord connect the PTO generator to the house. BTW I agree with the comments on strain releif using NM.
Top
#161740 - 04/07/07 06:24 AM Re: Romex and Extension Cords [Re: Ann Brush]
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
That one's a classic... I just took two extension cords made with German NYM out of service at the local church.
Top
#161756 - 04/07/07 10:08 AM Re: Romex and Extension Cords [Re: BubbaJohn]
Elviscat Offline
Member
Registered: 08/13/05
Posts: 214
Loc: Seattle Washington USA
I'd say it's the shape and flexability issues i.e. it pulls out of connectors too easily and is pretty useless as an extention cord because it's too inflexible, plus I doubt that the solid wire has as high a pull-out force from the connector itself, though this is just conjecture. I think that the romex jacket durability v.s. extention cord durability is a fairly minor issue.

-Will
Top
#161766 - 04/07/07 12:23 PM Re: Romex and Extension Cords [Re: Elviscat]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
This is one my wife took away from a trade ... wait for it ...
Electricians!


_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals