#161285 - 04/01/07 07:11 AM R.V . Park Calculations
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
7 sites on a Feeder in a RV park with a (Total of 35 sites in the park.) This feeder has 9600VA then 80ft 9600VA then 80 ft then 5 3600VA sites each 100 ft apart then 100ft to the breaker . Alum. wire.
9600-80' 9600-80' 3600-100' 3600-100' 3600-100' 3600-100' 3600-100'feeder brk 100'
Alum wire Question size of wire , Size of Feeder Breaker? Checking myself here.
Breaker to last site 680 feet.
Thanks Guys The Yooper
Top
2017 / 2014 NEC & Related Books and Study Guides
#161309 - 04/01/07 12:49 PM Re: R.V . Park Calculations [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
No one wants to take a Crack at this one????
Top
#161313 - 04/01/07 01:04 PM Re: R.V . Park Calculations [Re: Yoopersup]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Ernie- I don't understand the problem. Maybe you could word it a little differently and I'll take a crack at it. What are the actual loads at each site and how lond are the runs? Maybe it's just me but I can't follow you. Sorry.
_________________________
George Little
Top
#161316 - 04/01/07 01:19 PM Re: R.V . Park Calculations [Re: George Little]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I think the problem with RV parks is the load changes every time they rent a spot. When I was still looking at these with state they had times when all the spots were using an appreciable portion of the allotted 50a. They originally assumed 50% but that was not a good number on a hot night when these land yachts had both A/C units going full blast and every light, TV and other doodad on.
_________________________
Greg Fretwell
Top
#161324 - 04/01/07 02:19 PM Re: R.V . Park Calculations [Re: gfretwell]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The size of the breakers is quickly determined by 551.73.

Figuring conductor sizes to compensate for voltage drop gets more complicated.

IMHO this is a time when I would figure voltage drop assuming 100% loading of the feeders.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#161329 - 04/01/07 03:39 PM Re: R.V . Park Calculations [Re: iwire]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I see where he is going now. The state was too dumb to actually adjust the size of the feeder as they went along.
This is something you could plug into an excel spread sheet and tune for load any way you want. Maybe Steve has something.
_________________________
Greg Fretwell
Top
#161332 - 04/01/07 05:11 PM Re: R.V . Park Calculations [Re: gfretwell]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
How did you get the loads? is the 3600 a 30a @ 120? That will change things a little. Putting the big loads at the end will cost you too. I am guessing 120v spots at 30a and 240v spots at 50a (using 40 for the load calc).
_________________________
Greg Fretwell
Top
#161333 - 04/01/07 05:58 PM Re: R.V . Park Calculations [Re: gfretwell]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
OK Yooper, here you go. If you start out with a 150a breaker the smallest wire will be 3/0 al. Use that for the first 80' hop from the end. You drop .8 volts. Then go 4/0, 4/0 4/0 for the next 80 and two 100' hops. That drops 1.2, 1.9v, and 2.2v respectively.
Then use 250MCM for the next two 100' hops dropping 2.1 and 1.7 respectivly. Run 350MCM back to the losd disconnect for another 1.9v.

I think that is 11.8v or just a shade under the 5%.
_________________________
Greg Fretwell
Top
#161335 - 04/01/07 06:20 PM Re: R.V . Park Calculations [Re: gfretwell]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
The 3600 watts comes out of the code book,see 551.73
Thats about what I came up with. I just wanted to make sure. The owner wanted the same size from start to finish so I went with 300 mcm in my Calcs.
Top
#161358 - 04/02/07 04:48 AM Re: R.V . Park Calculations [Re: Yoopersup]
john p Offline
Member
Registered: 11/02/06
Posts: 32
Loc: Bemidji,MN.USA
Its hard to find rv eguipment that you can loop any thing larger than 250's thru so use 250 mcm with a full size nutral. I use 250/250/4/0 USE direct burial and use the 4/0 as the ground, reidentify with green tape and run a single 250 with the group for the nutral and reidentify with white tape.
I would just start out with a 200 amp breaker hit a terminal box.The runs are to long to just use one feeder. so break it up and run multipal feeders from the terminal box.you may have to run a feeder all the way to the farthest pedistal just because of voltage drop. I hope this helps.

John P
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals