ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#161077 - 03/29/07 07:46 PM Washer Grounding
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
I have a picture of an old Kenmore washer, or rather, a ground connection on the back.

Any idea what this long ground wire is for? It has a ring-lug on the end. The label says: External Ground Connector. This is the way it was installed (now headed to the landfill.)

Ian A.
Theelectrikid

Top
Tools for Electricians:
#161081 - 03/29/07 08:37 PM Re: Washer Grounding [Re: Admin]
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
That's for use in grounding the washer to a cold water pipe or electrical box, if the outlet avaliable is not a 3 prong type.
Top
#161163 - 03/30/07 08:00 PM Re: Washer Grounding [Re: wa2ise]
yaktx Offline
Member
Registered: 02/19/03
Posts: 288
Loc: Austin, Texas, USA
This is one of several grounding methods that predate the widespread adoption of NEMA 5-15 devices. (Washers were among the first appliances to require equipment grounding.)

Another method is the cold water hose with steel wires braided into the rubber. It was specifically intended for the cold side. (This method wouldn't work for modern machines, which have a plastic solenoid valve body. It wouldn't work with plastic pipe, either.)

My dad told me he remembers when some towns expected washers to be grounded with a jumper as shown here. Likely as not, few users understood this, and when machines were moved, the ground was not reconnected.

I've heard that some jurisdictions, before the '96 NEC, required this type of jumper for dryers. The internal bonding strap had to be removed, and the NEMA 10-30 cord freed of a grounding connection. Imagine what happened when such a dryer was moved to another house... No more ground! I suspect the same happens when today's washers are moved from a NEMA 14 to a NEMA 10 location.
Top
#161286 - 04/01/07 07:39 AM Re: Washer Grounding [Re: yaktx]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Laundry receptacles were the first in dwellings to require an equipment ground, W-A-Y on back in the 1947 NEC.

From 2124 "Receptacle Outlets Required"




Whatever possessed the manufacturers to keep putting these jumpers on washing machines for so long escapes me.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals