#161065 - 03/29/07 06:49 PM meter main as sub
Niko Offline
Member
Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Hi folks,
I will be installing a new meter main and am using the existing meter main as a sub panel. Besides the obvious separate the grounding bar from the neutral bar, install a new GEC from the new panel, can the existing meter location be covered with a clear cover? Or the existing metermain be replaced with a regular subpanel?
Does the NEC address this or it a local AHJ decision?

Thank you
Edward
_________________________
Be kind to your neighbor, he knows where you live

Top
2017 / 2014 NEC & Related Books and Study Guides
#161067 - 03/29/07 06:54 PM Re: meter main as sub [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Either you reach a higher point today, or you exercise your strenght in order to be able to climb higher tomorrow.
Friedrich Nietzsche


Edited by Niko (03/29/07 06:55 PM)
Edit Reason: i tried to add as a signature.but went in as a reply
_________________________
Be kind to your neighbor, he knows where you live

Top
#161193 - 03/31/07 08:36 AM Re: meter main as sub [Re: Niko]
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
Neutral (grounded conductor) will be bonded in the old meter socket. As an inspector I would not allow it.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.
Top
#161199 - 03/31/07 09:00 AM Re: meter main as sub [Re: Alan Nadon]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I assume he is saying he will bypass or remove the meter connections and only use the disconnect with the cabinet as a J box. If he can isolate the bonding that should not be an issue but I still would question the suitability of the cover with nothing but that plastic "snap in" over the meter hole. They tend to fall apart pretty fast in the sun. If you screwed a metal cover over the hole I would not be too concerned.
_________________________
Greg Fretwell
Top
#161217 - 03/31/07 12:33 PM Re: meter main as sub [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Thank you for the replies,
Alan, i will isolate (unbond) the grounding and the grounded.
My only concern is the meter location and as suggested i may install a metal cover VS clear plastic.

Thanks again for the replies.
_________________________
Be kind to your neighbor, he knows where you live

Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 97 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals