The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 90 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#160704 - 03/24/07 03:53 PM Slipping conductors
myklein Offline
Junior Member

Registered: 03/23/07
Posts: 2
Loc: California/Arizona
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?

Top
#160706 - 03/24/07 04:37 PM Re: Slipping conductors [Re: myklein]
tshea Offline
Member

Registered: 11/22/03
Posts: 14
Loc: racine, wi
No code violation unless you overfill the conduit. More of a mechanical problem. Good luck!

Top
#160711 - 03/24/07 05:02 PM Re: Slipping conductors [Re: myklein]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Hi there myklien,
Welcome to ECN, mate!.
Personally (coming from a guy in New Zealand) I'd avoid drawing cables into a conduit that carries existing cabling, for the reason that if you aren't careful you can burn the insulation off of the existing cables by friction, you can use all the lube you like, but at the end of the day, you still have to be careful.
Bends in the conduit are where the most problems arise.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#160771 - 03/25/07 02:01 PM Re: Slipping conductors [Re: myklein]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Originally Posted By: myklein
Is there a code, I can't find it, that prohibits slipping new wires past existing wires in an existing conduit?


No, not an NEC one.

We do it quite often but like anything some commonsense must be used. You can not expect to slide a few new conductors in a conduit that is already loaded. Or as Mike said a conduit that is full of bends.

Many times the best way is to choose one of the existing conductors and use it as a pull rope.

If I need two new conductors I will tie three onto an existing conductor and pull that one out to pull the new ones in.

Go slow, again for the reason Mike pointed out, friction could burn through a stationary conductor.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#160801 - 03/25/07 09:27 PM Re: Slipping conductors [Re: iwire]
myklein Offline
Junior Member

Registered: 03/23/07
Posts: 2
Loc: California/Arizona
I'm a retired electrician, and have always advised against slipping wires because of the possibility of insulation burn. CalTrans California's Transportation entity has written in there standards wire is not to be slipped at any time.
I have seen it written into so many job specs that I thought it was also in the NEC.
Thank you to all that replied.

Top
#160809 - 03/26/07 04:12 AM Re: Slipping conductors [Re: myklein]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Armored cable (with braided wire armor) is great for this- the armor slides easily along other armored cables, and is very resistant to damage.