|
0 members (),
228
guests, and
10
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
OP
Administrator Member
|
Do alarm wires need connectors, or bushings, where thy enter boxes? This box, btw, is exactly as I found it; I was on-site to move a light, and had nothing to do with the alarm service. The cover was just as you see it.
- renosteinke
|
|
|
|
Joined: Dec 2002
Posts: 228
Member
|
Are you sure that is alarm wiring? I don't think I have ever seen thhn used for alarm systems, normally some multi conductor cable. I am pretty sure you need to have mechanical protection whenever any cable enters a splice box, at a minimum it is good workmanship.
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
On the strut to the side, you can see the box cover, which is labled "fire alarm."
While you can't see it in the pic, every panel for this building is less than eight feet away- and this mess doesn't go there.
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
The way that's wired certainly doesn't look like "good practice" to me.
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
Makes you wonder sometimes IF a fire has ever started, or could start from a malfunction in a fire alarm.. A.D
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Nope, not enough energy. And one way or the otherv it would end up in an Alarm condition.
|
|
|
|
Joined: Mar 2004
Posts: 16
Member
|
I'd put a bushing on just to keep the wires from getting too close to a grounded metal box. THHN wire is often used in FA applications in the Golden state,CA, and sometimes a a nick in the jacket will lead to ground faults,very frustrating to chase down. preevnt the problem before it becomes one.
|
|
|
Posts: 32
Joined: June 2004
|
|
|
|
|