#159799 - 01/30/05 02:00 PM running cat5e
dryden_burton Offline
Member
Registered: 11/24/04
Posts: 11
Loc: Maple Creek, Saskatchewan, Can...
is running cat5e in heating ducts alowed ?
_________________________
Dryden
Top
Study Guides for VDV / Structured Cabling Installers
#159800 - 01/30/05 02:12 PM Re: running cat5e
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Simple answer: No
Little more specific: you can go THROUGH, at ninety degrees. I would infer that cable should then be plenum rated.
Top
#159801 - 01/30/05 03:28 PM Re: running cat5e
dryden_burton Offline
Member
Registered: 11/24/04
Posts: 11
Loc: Maple Creek, Saskatchewan, Can...
i didnt think so
ok thanks
_________________________
Dryden
Top
#159802 - 02/01/05 01:18 PM Re: running cat5e
dstanford Offline
Member
Registered: 12/29/04
Posts: 23
Loc: Asheville NC USA
i don't think you can run through ducts even at 90 degrees... where did you see that at renosteinke. why that would be something to take a picture of and submit to the picture forum
Top
#159803 - 02/01/05 04:47 PM Re: running cat5e
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Not that its a great practice, it is allowed with some limitation. (With Plenum rated cable...)

Quote:
800.53 (A)Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CMP. Abandoned cables shall not be permitted to remain. Types CMP, CMR, CMG, CM, and CMX and communications wire installed in compliance with 300.22 shall be permitted. Listed plenum communications raceways shall be permitted to be installed in ducts and plenums as described in 300.22(B) and in other spaces used for environmental air as described in 300.22(C). Only Type CMP cable shall be permitted to be installed in these raceways.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#159804 - 02/01/05 05:15 PM Re: running cat5e
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Looks like I get smacked for "shooting from the lip." Apparently I was repeating something I'd heard, rather than actual code. Of course, you must forgive me, as I've never seen wiring in ducts (other than a short length to power something that was part of the duct system!).
300.21 and .22 seem to be the primary place where the NEC discusses wiring in ducts, with numerous other sections that boil down to "OK to run plenum rated wires in ducts." There ARE some other qualifications, so check it out.
Top
#159805 - 02/01/05 05:25 PM Re: running cat5e
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Reno, I'm not smacking anyone....

It is a horrible practice in my opinion though. I've seen it done, even been forced by an employer to do it myself once. I don't like it at all.

Seen this thread for a day or so, but was reluctant to answer. Wish it were not an actual code.

[This message has been edited by e57 (edited 02-01-2005).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals