The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 100 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#159690 - 01/12/05 09:31 PM prewire data for resi rough in
dougwells Offline

Member

Registered: 05/03/03
Posts: 1228
Loc: kamloops BC Canada
I have five data drops to install for a resi home in the rough in stage. How do i support the cat 5 as i hear its not a good idea to lay it on the rafters and how do we support the vertical runs.

Top
Study Guides for VDV / Structured Cabling Installers
#159691 - 01/13/05 02:26 AM Re: prewire data for resi rough in
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Follow simular rules of support and protection as you would for romex.

If you lay it on rafters in an accessable attic, some guy is going to have to crawl over them some day. (Get them caught in thier linemans as they shift by... Snip!)

An OK method of support in wood framing is to drive a romex staple 3/4's in, and loosly zip tie the cables to it.

For larger bundles that you might want to re-pull or add to later use dry rings, (Bridal rings) or J-hooks and leave a string. If you set up rings in way that the angle of attack at each is 30+/-degrees, you can pull more later most often.

Support with this stuff is more guidance than anything.

For vertical drops over 20' you should strain relief it by zip ties snuggly, but not too tight as to deform the jackets. Just enough to support the wieght of the cables.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#159692 - 01/18/05 09:10 PM Re: prewire data for resi rough in
trollog Offline
Member

Registered: 10/02/04
Posts: 273
Loc: San Diego California USA
For what it's worth, those are the same methods I have seen data guys employ in houses I have worked on.... if you were looking for a second opinion.. the advice is sound.