ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 17
Recent Posts
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,474 Are you busy
166,181 Re: Forum
160,635 Need opinion
Who's Online Now
1 registered members (gfretwell), 52 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#15708 - 10/25/02 11:26 PM bad practices  
Mike_Riverside  Offline
Member
Joined: Aug 2002
Posts: 33
can i get some input here...

we are working on "hotel style" apartments (retirement place), 74 units in this building. each unit has a 90 amp sub-panel. To feed these panels we ran 2-3 w/gnd sub-feeds. Some runs are as far as 350 feet from the meter room.

Anyways, to the point...the foreman had some helpers strapping the cables every 4 feet, the problem is they are doing the three at a time with zip ties and drywall screws!


Next, all the circits i ran in the corridors (12-2 and 12-3 MC Cable), the foreman had me "strap", all in a bundle, with 2 1/2", 2", or 1 1/2" EMT straps.

there is more... i will try to get som pics.

BTW this guy is the VP of the corperation.


Work Gear for Electricians and the Trades

#15709 - 10/26/02 07:57 AM Re: bad practices  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
hi Mike_Riverside.
[Linked Image]

Quote
2-3 w/gnd sub-feeds. Some runs are as far as 350 feet from the meter room.


I'm comming up with roughly 12 volts or 5% drop @ 240....blows the 210.19(A)FPN....

Quote
every 4 feet, the problem is they are doing the three at a time with zip ties and drywall screws!

hmmm, messy...
well ok ..T310.15(B)(2)(a) , given 310.15(B)(4) {kick's the noodles out} means 6 conductors @ 80%. , so per 310.16 starting @ 100a we get 80A.

~This is all assuming it's AL, and bundled per 310.15(B)(2)

~ The other issue is the tie wraps, i believe panduit had obtained a listing in recent years, but i'm not sure as to it's specifics.

~ The EMT straps may be an obvious listing violation to some (110.3(B))

~ 310.15(B)(2) Ex has an 02' change applicable to the derating of 'bundled' MC

[Linked Image]


#15710 - 10/26/02 05:07 PM Re: bad practices  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Maybe they should make up some trapeeze type hangers using Unistrut or Kilndorf, that way they can pull a lot of wires and support them properly. You might not have to worry about bundling either.


#15711 - 10/27/02 12:37 AM Re: bad practices  
ShockaRe  Offline
Junior Member
Joined: Oct 2002
Posts: 1
if the cables are tie wraped for more than 24 inches togethor, this is considered bundleing Thus you will now need to derate


#15712 - 10/27/02 09:15 PM Re: bad practices  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Mike, I was actually taught that the Romexes had to be separated in order to provide for heat dissipation by a Riverside County inspector. Have you had any inspections yet?
(I also cut all the ty-raps off of the wiring inside panels when I find them. They make for a very neat looking job, but when they're all bundled for 24" or more, as mentioned earlier, it becomes a derating problem)


#15713 - 10/28/02 01:39 AM Re: bad practices  
Mike_Riverside  Offline
Member
Joined: Aug 2002
Posts: 33
sparky: yes, they are AL

electure: we are actually working in Laguna Niguel right now. we have had an inspection, but only on the first floor of this building. All the sub-feeds are run from the meter room to the third (top) floor and then down to the panels on 3, 2, & 1 floors, so the inspector has not seen this yet.



Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7750 MB (Peak: 0.9181 MB) Zlib enabled. Server Time: 2017-03-26 05:29:37 UTC