#15708 - 10/25/02 08:26 PM bad practices
Mike_Riverside Offline
Member
Registered: 08/18/02
Posts: 33
can i get some input here...

we are working on "hotel style" apartments (retirement place), 74 units in this building. each unit has a 90 amp sub-panel. To feed these panels we ran 2-3 w/gnd sub-feeds. Some runs are as far as 350 feet from the meter room.

Anyways, to the point...the foreman had some helpers strapping the cables every 4 feet, the problem is they are doing the three at a time with zip ties and drywall screws!


Next, all the circits i ran in the corridors (12-2 and 12-3 MC Cable), the foreman had me "strap", all in a bundle, with 2 1/2", 2", or 1 1/2" EMT straps.

there is more... i will try to get som pics.

BTW this guy is the VP of the corperation.
Top
Work Gear for Electricians and the Trades
#15709 - 10/26/02 04:57 AM Re: bad practices
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
hi Mike_Riverside.


Quote:
2-3 w/gnd sub-feeds. Some runs are as far as 350 feet from the meter room.


I'm comming up with roughly 12 volts or 5% drop @ 240....blows the 210.19(A)FPN....

Quote:
every 4 feet, the problem is they are doing the three at a time with zip ties and drywall screws!

hmmm, messy...
well ok ..T310.15(B)(2)(a) , given 310.15(B)(4) {kick's the noodles out} means 6 conductors @ 80%. , so per 310.16 starting @ 100a we get 80A.

~This is all assuming it's AL, and bundled per 310.15(B)(2)

~ The other issue is the tie wraps, i believe panduit had obtained a listing in recent years, but i'm not sure as to it's specifics.

~ The EMT straps may be an obvious listing violation to some (110.3(B))

~ 310.15(B)(2) Ex has an 02' change applicable to the derating of 'bundled' MC

Top
#15710 - 10/26/02 02:07 PM Re: bad practices
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Maybe they should make up some trapeeze type hangers using Unistrut or Kilndorf, that way they can pull a lot of wires and support them properly. You might not have to worry about bundling either.
Top
#15711 - 10/26/02 09:37 PM Re: bad practices
ShockaRe Offline
Junior Member
Registered: 10/27/02
Posts: 1
if the cables are tie wraped for more than 24 inches togethor, this is considered bundleing Thus you will now need to derate
Top
#15712 - 10/27/02 05:15 PM Re: bad practices
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Mike, I was actually taught that the Romexes had to be separated in order to provide for heat dissipation by a Riverside County inspector. Have you had any inspections yet?
(I also cut all the ty-raps off of the wiring inside panels when I find them. They make for a very neat looking job, but when they're all bundled for 24" or more, as mentioned earlier, it becomes a derating problem)
Top
#15713 - 10/27/02 09:39 PM Re: bad practices
Mike_Riverside Offline
Member
Registered: 08/18/02
Posts: 33
sparky: yes, they are AL

electure: we are actually working in Laguna Niguel right now. we have had an inspection, but only on the first floor of this building. All the sub-feeds are run from the meter room to the third (top) floor and then down to the panels on 3, 2, & 1 floors, so the inspector has not seen this yet.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals