The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#155573 - 01/17/05 06:27 AM Bonding screw
rusty Offline
Junior Member

Registered: 12/22/02
Posts: 7
Loc: aurora, ne. usa
I just wondered if anyone wanted to speculate on something I saw the other day.

In a new steel storage building, a 200A Sq D panel was being fed directly from the meter. A grounding kit was installed in the panel. The GEC and bonding jumper to the steel building were the only wires on the grounding bar, and any neutrals were on the other (neutral bar). Conduit was run for all circuits with no EG. What caught my attention was arcing (just the marks) around the bonding screw. I checked the screw to see if it was tight, and turned it about 3 full turns.

I'm just wondering what caused this arcing. Did something short out to the conduit and return to the panel and arc between the screw and bar? I think I can imagine how this would happen, but would like to hear some ideas.

Thanks for all your help in the forum. I rarily post, but lurk everyday.

Top
Business, Office, Estimating, Legal:
#155574 - 01/17/05 06:36 AM Re: Bonding screw
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Welcome to the forum, rusty.

The most likely cause of the arcing is part of the neutral current is flowing through the GECs (probably the water line) back to the power company transformer.

This is normal and now that you tightened the screw you are all set.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts