#154539 - 03/13/07 02:02 PM allied 1099 boxs
big guy Offline
Member
Registered: 12/19/03
Posts: 59
Loc: pa
HI
I am working on town homes and would like to know if the opening on a 1099 allied box should be sealed in a fire wall.

1099 boxs are 2hr rated but ones you put wires in the box there will be a open area around the wire.

If I do need to seal this box could I get the info that says that I have to do this.

thanks
matt
Top
Building Codes & Related References
#154540 - 03/13/07 08:57 PM Re: allied 1099 boxs
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
If I read this right you need a putty pad to establish the fire rating
_________________________
Greg Fretwell
Top
#154541 - 03/14/07 04:12 AM Re: allied 1099 boxs
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
It sounds to me from that listing like the putty pads are only required if you don't meet the minimum separation of boxes. Am I reading that wrong?

The UL listing mentions several times that the gap between the box and the wall must be less than 1/8"- sounds to me like it's implying that some gaps less than 1/8" are acceptable, and cable entries may not need any special sealing.
Top
#154542 - 03/14/07 11:08 AM Re: allied 1099 boxs
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Yes you are right Steve. The joys of fire rated assemblies ;(

I was reading the wrong assembly description.
_________________________
Greg Fretwell
Top
#154543 - 03/14/07 01:05 PM Re: allied 1099 boxs
big guy Offline
Member
Registered: 12/19/03
Posts: 59
Loc: pa
I found it. thanks for the help


http://www.alliedmoulded.com/outlet_fireFAQ.cfm
Top
#154544 - 03/18/07 09:52 AM Re: allied 1099 boxs
Mark20 Offline
Member
Registered: 03/17/07
Posts: 25
Loc: Maryland
if you install 2 boxes in the same stud space of a dimizing wall-- one in "townhome a" and the other in "townhome b" then you would need putty pads for sure. as long as there's only one box in each stud space you shouldn't. at least that's how it's done in washington d.c. is that how everyone else sees it?
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals