#154388 - 07/02/05 06:03 PM Jacuzzi
bwise121 Offline
Member
Registered: 09/11/03
Posts: 114
Loc: Sacramento, CA USA
I'm installing a 240V 50Amp Jacuzzi at a residence. What is the minimum/maximum distances for the disconnect? Where can I find this in the NEC?

Many thanks,
Byron
Top
Building Codes & Related References
#154389 - 07/02/05 06:50 PM Re: Jacuzzi
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Article 680.40 states: Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

So, in short, the disco must be within sight and at least 5' away from the hot tubs inner wall, and not more than 10' away.
Top
#154390 - 07/02/05 07:00 PM Re: Jacuzzi
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Within sight but at least 5 feet away.

680.40 General.
Electrical installations at spas and hot tubs shall comply with the provisions of Part I and Part IV of this article.

680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be accessible and within sight from its equipment.

680.22 ...
(C) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.
_________________________
Greg Fretwell
Top
#154391 - 08/02/05 06:15 PM Re: Jacuzzi
livetoride Offline
Member
Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
Make sure to check with your local building Dept. They change the rules some places. We get a print out from the local bld. dept. when pulling permits for spas that are a little differant than code. Rod
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 68 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals