The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (jraef), 135 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#154291 - 01/25/05 10:52 PM Fire-stopping at multiple conduit penetrations.
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Anyone have any good ideas on how to penetrate firewalls with lets say a trappeze of 30+ 1/2" conduits with 1 1/8 spacing in an existing 2 hour wall?

Is there a fast way to do this?
Mark Heller
"Well - I oughta....." -Jackie Gleason

Building Codes & Related References
#154292 - 01/26/05 07:07 AM Re: Fire-stopping at multiple conduit penetrations.
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Mark, you may want to check out these pillows from 3M.

There are other products made by Rectorseal, Flame Stop, Hilti, to name a few.


#154293 - 01/26/05 08:19 AM Re: Fire-stopping at multiple conduit penetrations.
sandsnow Offline

Registered: 09/21/04
Posts: 163
Loc: Irvine, CA, USA
The best way to make the penetration is to call Hilti, 3M, Spec-Seal, etc. and tell them what you are penetrating and what you want to put through it. You will 99.9 % probably find that 30 plus will not be covered by a UL classified system. It sounds like it will probably be too large. New systems are being developed all the time, so I just might be wrong. You may be able to get through with one or more penetrations of multiples.

If you or the AHJ will accept it you can probably get some kind of engineering judgement from the manufacturer on this configuration. We do not accept "EJ's" because they do not comply with the Building Code.

I've looked at many penetrations through fire resistive construction, and the best advice I can give anyone is to plan the penetration with a manufactur rep BEFORE running the conduit through the wall or floor. Trying to find a system to match what you have done is hard.

I'm sorry there is no easy answer to your dilemna.
Larry LeVoir
City of Irvine, CA