The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/23/16 11:04 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
1 registered (LongRunner), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#154139 - 05/18/04 10:25 AM parking garage
jballa3844 Offline
Junior Member

Registered: 05/18/04
Posts: 1
Loc: carlstadt,n.j. usa
i need info on emergency lighting and exit signs when and where they are needed in parking garages, public and private. thanks

Building Codes & Related References
#154140 - 05/18/04 08:40 PM Re: parking garage
George Corron Offline

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
You're not getting replies because setting an egress path is a very trick thing. It is usually handled by an FPE (Fire Protection Engineer) and they are usually very good at what they do.

The rules are in the BOCA code, and the IBC, but they pretty much reference NFPA 101. Exit lights - head 'em toward the danged exit usually within 75', but LOTSA variables on that.

Emergency egress path must be lit to a minimum of 1 fc at the FLOOR level. You can handle this with batteries, UPS system, or even a genset.

If you use a genset in place of batteries, it must have a 90 minute fuel supply ON SITE, (Natural gas can not normally fulfill this requirement and requires approval of the AHJ) AND be ON LINE within 10 seconds of power failure, that is from 700-12, but you will also find it in NFPA 101, and 110.

Asking a generic question like that leaves way too many variables. Also, you're fire marshall must approve this path, they can probably help you out to establish this if you are going to take on the responsibility yourself.