The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 236 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#154059 - 02/20/04 08:02 PM Trenching Concrete Floors
Joey D Offline
Member

Registered: 10/10/03
Posts: 263
Loc: Arlington MA U.S.
I am on a job in a apartment building where the floors are all concrete. The contractor is framming a few areas in he middle of the ceiling to install recesed lights in. He has cut a 2inch deep trench in the ceiling from one lowered ceiling to the new one. The floors are only 8" deep. Would this be a smart thing to do?

Top
Building Codes & Related References
#154060 - 02/20/04 09:09 PM Re: Trenching Concrete Floors
crash Offline
Member

Registered: 10/21/03
Posts: 130
Loc: Calgary Canada
The only person who could answer that question is the Engineer who designed the building. If the engineer gave the contractor the go-ahead for this trench and the corresponding repair, then it should be okay.

Top
#154061 - 02/21/04 02:36 AM Re: Trenching Concrete Floors
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I agree with Crash.

Any chance these are precast cement decks?

If yes as long as the pre-stressed cables inside are not cut it seems you can do a lot to them, with an engineers OK.

Without an engineers OK this sounds dangerous.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#154062 - 02/21/04 07:05 AM Re: Trenching Concrete Floors
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
I agree with Crash and Iwire. A structural engineer would need to be involved, and it would seem to me that there would be some specific instructions to the cutting.

Roger

Top
#154063 - 02/21/04 07:54 AM Re: Trenching Concrete Floors
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
I was going to ask if they were Spancrete, or another type of cellular concrete. Taking 2" out of that could be, uh, problematic.

Get a Structural Engineer's opinion.

Top
#154064 - 02/21/04 09:20 AM Re: Trenching Concrete Floors
u2slow Offline
Member

Registered: 09/18/03
Posts: 198
Loc: Salt Spring, BC, Canada
I work in mainly new highrise construction. Typical floors are 190mm (approx 7-1/2") and having to chip a shallow trench in the ceiling or floor (to bury BX cable or 1/2" ENT) has not been an issue with the engineers or inspectors so long as the steel isn't cut. Usually we don't have to go deeper than 1" or so, unless there's a spot where the rebar is too shallow and we have to go behind it.

Check with YOUR engineer first though

[This message has been edited by u2slow (edited 02-21-2004).]

Top
#154065 - 02/21/04 04:31 PM Re: Trenching Concrete Floors
Joey D Offline
Member

Registered: 10/10/03
Posts: 263
Loc: Arlington MA U.S.
Thanks. I was thinking the same.

Top