#154034 - 02/13/04 09:57 AM Smoke detectors required?
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
I'll admit my ignorance upfront, but all of the clients that I have worked for in the recent past, took my recommendation for smoke detection in various areas without being challenged.
This client has a data center in a jurisdiction in which they follow the IBC. We have a sprinkler system throughout per NFPA 13. There are manual pull stations and audible/visual devices throughout. The occupancy is "Business".
There is smoke detection installed in many areas of the building but not all.
Here's the questions,
Is smoke detection required?
Since there is smoke detection installed in various areas of the building, must the entire building be covered in the same fashion for consistency based on NFPA 72?
Is there an exception, not requiring smoke detection if there is NPFA 13 sprinklers installed?
_________________________
Ron
Top
Building Codes & Related References
#154035 - 02/13/04 10:15 AM Re: Smoke detectors required?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Besides special buildings such as atriums, undergound buildings and high rise buildings, I see nothing in the IBC that requires detection for garden variety group "B" occupancy building.

A manual fire alarm system is required for group "B"'s with an occupant load over 500 persons or more than 100 persons above or below the highest level of exit discharge, there is also an exception for this for a sprinklered building.

I have never laid eyes on the NFPA 13 or NFPA 72, so they might contradict what I'm saying.

The thing about a group "B" occupancy, from a code point of view, is that provisions are quite lenient compared to the other major occupancy groups. For example, a typical office building never requires sprinkler sytems, unless for specific reasons (such as area increase, atrium, high rise, underground, etc.).

I hope this helps you Ron, but I'm not sure that it does
_________________________
Ryan Jackson,
Salt Lake City
Top
#154036 - 02/13/04 10:31 AM Re: Smoke detectors required?
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
Would you happen to have a suggestion for where to look for the exception to detection when there is sprinkler?
_________________________
Ron
Top
#154037 - 02/13/04 10:53 AM Re: Smoke detectors required?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Hi Ron. I just got off the phone with our Fire Marshall (and you might consider doing the same), and he tells me that the NFPA 72 is the document that applies.

From what he tells me, if you are sprinklered throughout, the only smoke detector you need is to be located in the same room as the fire alarm control panel, usually right above it, and it must be wired into the control panel. Beyond that, they are not required.
_________________________
Ryan Jackson,
Salt Lake City
Top
#154038 - 02/14/04 03:50 PM Re: Smoke detectors required?
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
OK, appears that Occupancy B building does not require smoke detection other than the control panels (as mentioned). The other smoke detection installed in 95% of the building is considered "non required coverage". NFPA 72 is confusing regarding this, as in the first article it says, if it is non required or not, you must comply with this code. Which implies that you have to install throughout anyway.
Then the second paragraph says, install them where you want, and coverage of the rest of the space or building is not required.
It's almost like these two paragraphs conflict, or should have been in the same paragraph to have one qualify the other.
_________________________
Ron
Top
#154039 - 02/15/04 02:35 PM Re: Smoke detectors required?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Ron...wait a minute now, are you telling me that a document written by the NFPA isn't easy to follow....I can't believe that :-P

I'm glad you were able to get your answer.
_________________________
Ryan Jackson,
Salt Lake City
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, HotLine1), 90 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals