The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Ruben Rocha), 96 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#153816 - 12/12/03 05:57 PM Cliffhanger
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Does this comply?

_________________________
Ryan Jackson,
Salt Lake City

Top
Building Codes & Related References
#153817 - 12/12/03 06:32 PM Re: Cliffhanger
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Great pictures. In the first one, I wonder if the POCO thinks the meter reader has easy access to the meter.

In the second one torpedo level comes to mind.

Roger

Top
#153818 - 12/12/03 07:32 PM Re: Cliffhanger
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Like Roger said, great pictures!

Are they going to raise the grade all along the side of the house, or is that it?

Maybe they should leave the scaffold there for the meter reader.

Or put a railing up ...

Bill

Top
#153819 - 12/12/03 07:49 PM Re: Cliffhanger
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Thats the finished product Bill.

The retaining wall is constrcucted on the property line. One of the many challenges faced when you build on the mountain.

I red-tagged the job and cited working clearance. The gaurd rail is an option, but I really don't want that panel right there.

Question: How does the NEC address the surface of the required working clearance? Is it silent? Can you stand on jagged boulders? Hmm....
_________________________
Ryan Jackson,
Salt Lake City

Top
#153820 - 12/12/03 07:58 PM Re: Cliffhanger
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Ryan,

I don't know any code section that requires solid footing in front of equipment. I thought about making a proposal on that for the 2005 NEC, but didn't get around to it. It should be common sense I think.

If there was such a rule it could also affect Panelboards and equipment installed in stairways.

Bill,

Top
#153821 - 12/13/03 04:11 AM Re: Cliffhanger
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Ryan I don't se working clearance as an issue here. As Bill said there is nothing about working surface. I don't think you could fail this. The poco may have the authority to disallow this (maybe won't energize?) if it does not conform to their specs.

Top
#153822 - 12/13/03 07:46 AM Re: Cliffhanger
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Ryan,

Is there nothing in the Building Code about guarding from falls, etc? If I put in a small fish pond on my front lawn that is 12" deep I'd have to put a fence around either it or the whole yard with a self-latching gate.

Maybe the POCO would have something to say if you point out the possible danger to their employees.

Bill

Top
#153823 - 12/13/03 08:07 AM Re: Cliffhanger
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
How does the local building code treat the edge of the yard at the top of the retaining wall? Are you allowed to roll a car, un-impeded, over the edge and into the neighbor's yard?
_________________________
Al Hildenbrand

Top
#153824 - 12/13/03 08:21 AM Re: Cliffhanger
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
What about 6'7" maximum to the OCPD.

And isn't the idea of 3' working clearance that you can step back 3' from the equipment?

Unless you feel like taking a fall you can not step back 3' here.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#153825 - 12/13/03 08:58 AM Re: Cliffhanger
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Ryan, Along the lines of Bill's and Al's post.

I can't tell for sure but it appears as though there is a crevice between the two levels.

If a person (especialy a child) were to fall could they be trapped?

I agree with Bob that the three foot clearance should be a flat surface.

whether specifically written into the code or not, our local inspectors require a flat unobstructed surface for this area.


Roger