ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 16
Recent Posts
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
TRUE POWER
by jraef. 03/21/17 09:13 PM
WEG CFW-11 Frequency Inverter
by jraef. 03/21/17 08:50 PM
fuse rejectors
by HotLine1. 03/20/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,152 Are you busy
165,898 Re: Forum
160,446 Need opinion
Who's Online Now
0 registered members (), 51 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#15374 - 10/15/02 07:54 PM photocell nightmare  
flush  Offline
Member
Joined: Dec 2001
Posts: 12
nj
hello all, i was called out on a job that an hid fixture wasnt working. i checked it out and the ballest was bad,also a pretty old fixture,the guy just wanted me to replace it ....a 220v hid fixture ran with 12/2. my question is doesnt a photocell need a neutral and what are my options any help would be apprecated ...thanks


Work Gear for Electricians and the Trades

#15375 - 10/15/02 08:25 PM Re: photocell nightmare  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Do they make a 220 volt photocell?


#15376 - 10/15/02 10:07 PM Re: photocell nightmare  
nesparky  Offline
Member
Joined: Jun 2001
Posts: 642
omaha,ne
intermatic has one. Don't have my catalog now but have used one about 7-8 months ago.


ed

#15377 - 10/16/02 12:36 AM Re: photocell nightmare  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
http://www.fisherpierce.com/N7700.htm
N7790 "105-285V" rating is prevalent in lighting controls.


#15378 - 10/16/02 05:28 PM Re: photocell nightmare  
flush  Offline
Member
Joined: Dec 2001
Posts: 12
nj
but my question is does all photocells need a neutral.. on a standerd photocell you have a black,red, and a white lead ....i dont have a neutral in the box. do they make a photocell that doest need a neutral?


#15379 - 10/16/02 06:00 PM Re: photocell nightmare  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
flush, please elaborate...do you mean are there 2-wire photocells? Not familiar with sny.


#15380 - 10/16/02 06:26 PM Re: photocell nightmare  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
Flush - If you use a 240V photo control on at 240V fixture you do not need a neutral. The voltage rating of the photo control is the rating of the heater that controls the bi-metal switch. Most manufactures have 120V rated photo controls and 208V - 277V rated controls. As far as I know all of them have black, red and white leads. The black is line, red is the load and the white gets connected to the neutral on a 120V or 277V circuit or to the other line on a 208V or 240V circuit.

Curt


Curt Swartz

#15381 - 10/16/02 08:58 PM Re: photocell nightmare  
flush  Offline
Member
Joined: Dec 2001
Posts: 12
nj
ok great thanks for your help .


#15382 - 10/17/02 08:28 PM Re: photocell nightmare  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Here is where the electronic age gets tricky. If your device (photocell, timer, motion sensor, etc.) does not have a neutral wire, it is doing one of the following:
-letting a minute amount of current flow through your load (light) all the time; if this is the case, having more than one such device in the circuit will cause problems; or,
-the device uses the ground path as a neutral. If this is the case, the device will not work properly if the ground path is poor (or non-existent, as with k&t wiring).


#15383 - 10/17/02 09:08 PM Re: photocell nightmare  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
John

If the photo cell only has 2 wires then what you say is true about a minimum/maximum load. Most photo cells have 3 wires but the third wire does not have to be a neutral. If you are using the photo cell on a 120 or 277 volt fixture then the third (white) wire gets connected to the neutral but if the fixture is 208 or 240 volt then the third wire (still usually white) gets connected to the other line wire feeding the fixture.

Curt


Curt Swartz


Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.8056 MB (Peak: 0.9793 MB) Zlib enabled. Server Time: 2017-03-23 02:12:16 UTC