#15372 - 10/15/02 07:31 AM Service Lateral
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
A service lateral originating at the Power Company pad mounted transformer secondary terminals will be installed in PVC. Voltage system is: 277/480V, 3Ph, 4W.
Am I correct in thinking an equipment grounding conductor is not required from the transformer to service disconnect.
I don't think it is a requirement.

Frank

[This message has been edited by Frank Cinker (edited 10-15-2002).]
Top
Work Gear for Electricians and the Trades
#15373 - 10/15/02 08:19 AM Re: Service Lateral
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Frank,
You are correct, an EGC is not required on the line side of the service disconnect. The grounded conductor is used for all equipment grounding on the line side and within the service disconnect enclosure.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals