The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 100 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#15356 - 10/14/02 01:27 PM Where do like your GFCI?
mamills Offline
Member

Registered: 11/30/01
Posts: 739
Loc: Wharton, Texas, USA
Hi All;
I hope this question doesn't come across like some of the DIY's which have appeared in the past...here goes:
In our community theater here, we have a small sump pump installed to discharge ground water seepage which accumulates in a small sump next to the orchestra pit (the lowest place in the building, about 6 feet below outside grade level). I am planning to install a new dedicated GFCI circuit just for the pump. Presently, it is connected to an ordinary lighting/receptacle circuit with other "stuff" backstage. The question; cost not withstanding, do you prefer a receptacle-type GFCI or a circuit breaker type (in this case, a SqD QO type). At face value, it seems like the circuit breaker type would be better or more reliable. Any thoughts from the pro's?

Mike (mamills)

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#15357 - 10/14/02 02:09 PM Re: Where do like your GFCI?
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I will answer your question with a question. Why are you using a gfci for this application. You are setting yourself up for potential problems. If this motor causes nuisance tripping on the gfci you might have a flooding situation on your hands.

Top
#15358 - 10/14/02 02:34 PM Re: Where do like your GFCI?
mamills Offline
Member

Registered: 11/30/01
Posts: 739
Loc: Wharton, Texas, USA
My reasoning for the GFCI relates to the location of the sump. It is in an area backstage, but right next to the orchestra pit. The discharge pipe out of the pump is about 1 1/4" steel. It comes out of the sump hole through a steel cover plate, then turns 90 degrees and is coupled to a PVC pipe which leads out of the building. During certain times of high humidity, this backstage floor area sweats. I was concerned about people standing on this floor and making contact with the discharge pipe or the cover plate. We have not had any problems yet (other than people accidentally turning off the pump along with a couple of other lighting circuits which terminate in the breaker panel.

Would I be better off simply re-plumbing the pump with PVC pipe throughout, since the pump does have an EGC?

Mike (mamills)

Top
#15359 - 10/14/02 02:35 PM Re: Where do like your GFCI?
txsparky Offline
Member

Registered: 05/25/01
Posts: 578
Loc: Magnolia,.Texas U.S.A.
I would install a single receptale for the sump pump,not gfci protected.
_________________________
Donnie

Top
#15360 - 10/15/02 03:57 AM Re: Where do like your GFCI?
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
to GFI or not to GFI, that is the question?
(shakespearian chortle...)

well, we're not required by code, yet some people up my way with the stone foundation/ wading pool option do make me nervous
, so yes , i have put sumps on GFI's.

But i will include something else, like the cellar lights on the circuit, in lieu of fancy alarms/indicators etc....

after all..the show must go on...

Top
#15361 - 10/15/02 06:16 AM Re: Where do like your GFCI?
mamills Offline
Member

Registered: 11/30/01
Posts: 739
Loc: Wharton, Texas, USA
Sparky:
Also, if the pump fails, it would be a good place for an orchestra to perform Handel's "Water Music"

Mike (mamills)

BTW...actually, the building doesn't leak QUITE that much...

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals