#152761 - 12/21/05 08:24 PM Bull-Dog Equipment
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
We will be re-habing this next month. Appears to be in fair condition. Anything specific we need to look for? (i.e. replacing push-o-matic breakers, re-tourquing etc.)

- LearJet9











Top
Super Rod Cable Installation Tools

Super Rod Cable Rod System
Super Rod Cable Rod System -
Voted
Best Product of the Last 50 Years by members of NICEIC

#152762 - 12/22/05 05:51 AM Re: Bull-Dog Equipment
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
On a quick look, the grounded conductors and the Equipment grounding conductors are on the same bus...is this the service disconnect, or downstream of it?
_________________________
Pierre Belarge

Top
#152763 - 12/22/05 08:46 PM Re: Bull-Dog Equipment
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
This could be service equipment if you can deenergize the entire service with six throws of a 2 x 12.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#152764 - 12/27/05 05:15 AM Re: Bull-Dog Equipment
LearJet9 Offline
Member

Registered: 04/24/05
Posts: 196
Loc: Millis, MA USA
Immediatly to the left of what you can see in the main disconnect, 800A I beleive. We will be replacing about 100 push-o-matic devices and checking all connections for tightness. We will of course address any other issues we find while in there. The guys working on this job have never seen bull-dog equip before.

Top
#152765 - 12/27/05 05:47 AM Re: Bull-Dog Equipment
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
How many pole positions are in the common backbox, >42?
Will you replace the guts with a new panelboard with individual backboxes. I was in a jurisdiction that would allow the reuse of a old backbox for new panelboard guts (not UL listed together).
_________________________
Ron

Top
#152766 - 12/27/05 11:33 AM Re: Bull-Dog Equipment
LearJet9 Offline
Member

Registered: 04/24/05
Posts: 196
Loc: Millis, MA USA
Each seperate section has 40 positions in 2 banks. Each section is controlled by 2 contactors, 1 for each bank of 20 devices. As far as I know at this time, we will only be replacing individual devices, and then only about 80 out of 120. (?) We will be checking all terminations to make sure they are secure. Panel schedules are all incorrect but they declined to have us do a new panel schedule.

Top
#152767 - 12/27/05 08:39 PM Re: Bull-Dog Equipment
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
In pic #3, are you going to replace the GE and FPE breakers?

P.S. The subject of mixing different manufactures breakers in the same enclosure would be a good thread all by it self.

Top
#152768 - 12/28/05 01:32 AM Re: Bull-Dog Equipment
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Just a little question,
How did it get the name Bull-Dog?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#152769 - 12/28/05 04:19 AM Re: Bull-Dog Equipment
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
You need to get rid of that aluminum ladder before someone gets hurt.

Top
#152770 - 12/28/05 07:26 AM Re: Bull-Dog Equipment
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
Bulldog electric,it was a I-T-E subsiduary, now part of Siemens.


BTW, its "Pushmatic"

Top