#15251 - 10/10/02 08:10 PM class 2 div 2 fittings
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
sealtight? waterproof? if i look in my truck boxes for a fitting, what do i look for? what qualifies in the class 2 div 2 zone?
Top
Work Gear for Electricians and the Trades
#15252 - 10/10/02 08:40 PM Re: class 2 div 2 fittings
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Cindy,
Standard sealtight and fittings are fine for Class 2 Div 2. In Class 2 we aren't trying to contain an explosion like we are in Class 1, all we are trying to do is to keep the dust out of the electrical equipment and keep the electrical equipment surface temperature far below the ignition point of the dust involved.
Don
_________________________
Don(resqcapt19)