#150761 - 10/15/05 07:49 PM Osha vs NEC
mbarnwatt Offline
Junior Member
Registered: 04/25/04
Posts: 1
Loc: Centennial, Colorado, USA
In Denver, we have recently run into an interesting problem with our local utility. Of course, the NEC requires
'230.24 Clearances
Service-drop conductors shall not be readily accessible and shall comply with 230.24(A) through (D) for services not over 600 volts, nominal.
(A) Above Roofs Conductors shall have a vertical clearance of not less than 2.5 m (8 ft) above the roof surface. The vertical clearance above the roof level shall be maintained for a distance of not less than 900 mm (3 ft) in all directions from the edge of the roof.'
Our utility provider, Xcel, has told us they can not hook-up these services because OSHA has prohibitted them from connecting to anything more than 5' above a "walkable roof" and a ladder on a roof is unacceptable. Needless to say, we have had to install several 9' masts with a point of attachment at 8.5' due to 230.24(A), have the AHJ inspect them, then lower the mast knob to 5', have the utility attach the service drop, then (third trip) push the mast knob back up to the required 8.5'. ????
Are there any others out there with similar problems and, if so, what have been your solutions, and if not, any comments?
Top
Arc Flash PPE Clothing, LOTO & Insulated Tools
#150762 - 10/15/05 08:14 PM Re: Osha vs NEC
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
mbarnwatt,

Welcome to ECN,
I never had to do it, but our local utility allows a "Drop Swing" Service where the point of attachment is inaccessible (by their rules).

Maybe something along these lines would be acceptable. Look at Drawing D9 (page 11) in the following file:
http://www.lipower.org/pdfs/commercial/redbook/Chapter11.pdf

Bill
Top
#150763 - 10/27/05 06:56 PM Re: Osha vs NEC
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
mbarnwatt,

Welcome to ECN, mate!.

This is a rather interesting topic.
Let's bump it back up to the top.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals