#150083 - 09/07/04 05:02 PM ppe for service tie in  
nov  Offline
Member
Joined: Aug 2004
Posts: 69
New Jersey
I was just wondering what type of PPE do you guys use when doing a residential service tie in. Here in NJ you do the tie in live and the crimp or split bolts stay on the power company does not redo them for the most part I believe


Arc Flash PPE Clothing, LOTO & Insulated Tools

#150084 - 09/07/04 10:50 PM Re: ppe for service tie in  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I wear gloves and safety glasses and lay off the caffeine. Either on the roof or a fiberglass ladder. It must be dry.

Dave


#150085 - 09/08/04 06:57 PM Re: ppe for service tie in  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
the POCO lets you do your own cut over?? [Linked Image] our power company won't even let us pull the meter!


[This message has been edited by trekkie76 (edited 09-08-2004).]


#150086 - 09/08/04 09:01 PM Re: ppe for service tie in  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
According to NFPA 70E Table 130.7(C)(9)(a), if the short circuit current available is 25kA and the protective device has a 0.03 second (2 cycle) fault clearing time when compared to the device characteristic curve, a category 1 PPE is required with voltage rated gloves and tools. For < 10 kA short circuit current available, the hazard/risk category required may be reduced by one number.
Since it is not likely that the upstream protective device (utility fuses) will clear in 2 cycles or less, considering that the arc flash may occur at the meter, you would have to perform a detail calculation from 70E, probably resulting in a higher level PPE.


Ron

#150087 - 09/09/04 06:39 PM Re: ppe for service tie in  
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
Unfortunately, ComEd requires us to do this live. On my very first 200-amp overhead service, I called for them to disconnect. I was told to do it live myself. I said something like "No, really, I can be here anytime". He said something like "It's your job". They will disconnect for underground services, but not overhead. Typically they come by later to crimp their connectors on. Once I moved the service across the house and draped temporary wires across the roof. I'd love to have a POCO disconnect for me.

Dave



Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7668 MB (Peak: 0.9037 MB) Zlib enabled. Server Time: 2017-03-31 00:28:44 UTC