The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 218 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#150083 - 09/07/04 02:02 PM ppe for service tie in
nov Offline
Member

Registered: 08/08/04
Posts: 70
Loc: New Jersey
I was just wondering what type of PPE do you guys use when doing a residential service tie in. Here in NJ you do the tie in live and the crimp or split bolts stay on the power company does not redo them for the most part I believe

Top
Arc Flash PPE Clothing, LOTO & Insulated Tools
#150084 - 09/07/04 07:50 PM Re: ppe for service tie in
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I wear gloves and safety glasses and lay off the caffeine. Either on the roof or a fiberglass ladder. It must be dry.

Dave

Top
#150085 - 09/08/04 03:57 PM Re: ppe for service tie in
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
the POCO lets you do your own cut over?? our power company won't even let us pull the meter!


[This message has been edited by trekkie76 (edited 09-08-2004).]

Top
#150086 - 09/08/04 06:01 PM Re: ppe for service tie in
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
According to NFPA 70E Table 130.7(C)(9)(a), if the short circuit current available is 25kA and the protective device has a 0.03 second (2 cycle) fault clearing time when compared to the device characteristic curve, a category 1 PPE is required with voltage rated gloves and tools. For < 10 kA short circuit current available, the hazard/risk category required may be reduced by one number.
Since it is not likely that the upstream protective device (utility fuses) will clear in 2 cycles or less, considering that the arc flash may occur at the meter, you would have to perform a detail calculation from 70E, probably resulting in a higher level PPE.
_________________________
Ron

Top
#150087 - 09/09/04 03:39 PM Re: ppe for service tie in
Dave55 Offline
Member

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
Unfortunately, ComEd requires us to do this live. On my very first 200-amp overhead service, I called for them to disconnect. I was told to do it live myself. I said something like "No, really, I can be here anytime". He said something like "It's your job". They will disconnect for underground services, but not overhead. Typically they come by later to crimp their connectors on. Once I moved the service across the house and draped temporary wires across the roof. I'd love to have a POCO disconnect for me.

Dave