The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#149821 - 04/25/04 05:33 AM Power Tool testing?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
You guys have your Drills, Grinders and Power Saws, but at the end of the day, how often are these tools or the flex's on them checked for damage?.
Once a month?, Once a year?, never?, or when someone gets a shock off them?.
Power tools as essential as they are, need to be tested regularly, to ensure thier own safety and those that use them!.
How often are your tools tested?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
Arc Flash PPE Clothing, LOTO & Insulated Tools
#149822 - 04/26/04 07:53 PM Re: Power Tool testing?
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
Mike
The company that I work for now, has us use our own tools for the most part.. I inspect my tools everytime I open the case, before I put them to use Company's that I've worked for in the past, check the tools out for these types of concerns each time it passes through the shop on its way to another jobsite.. Not to mention that if we'd spotted something that was amiss, we were to report it, so the company driver could pick the tool up & take it for repairs or for a meet with a dumpster..

-Randy

Top
#149823 - 04/30/04 02:59 AM Re: Power Tool testing?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Randy,
Thanks for your response, but what I was looking for was those that used a PAT tester, for all of the Company Tools and the ones that are brought in for testing.
Unless you have an OSH approved Tag here, that Power Tool is not allowed to be used on that site.
It states that it has been tested within the last 12 months.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#149824 - 04/30/04 03:09 AM Re: Power Tool testing?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
What I mean't Guys,
Was this could be a real venture for you guys that hold licences.
Get a PAT (Portable Appliance Tester) and tag each appliance with your test results and you can have your Co. Identity on the tag too!, especially for re-test purposes, people that work where these bits of equipment are used would read your name on there.
We do HEAPS of this sort of business, BELIEVE ME!.
This is why we are so Flat Out!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#149825 - 07/28/04 06:40 AM Re: Power Tool testing?
Big Ed Offline
Member

Registered: 04/07/04
Posts: 56
Loc: Roxboro, NC, USA
OSHA requires that all portable equipment be checked quarterly for ground integrity, we use that check to full inspections on the equipment.

OSHA also states:
1926.404(b)(1)(iii)(C)
Each cord set, attachment cap, plug and receptacle of cord sets, and any equipment connected by cord and plug, except cord sets and receptacles which are fixed and not exposed to damage, shall be visually inspected before each day's use for external defects, such as deformed or missing pins or insulation damage, and for indications of possible internal damage. Equipment found damaged or defective shall not be used until repaired.

We have a significant problem here, in that the operators and mechanics see the colored tape (specific color for each quarter) on the cord and they assume that nothing can go wrong.

Even with a PAT, it only proves that the device was ok when it was checked. 10 minutes later some knot-head can have dropped it in a bucket of water.

No amount of scheduled testing should relieve the user from checking it each use, and not using it if it is damaged.

We had a mechanic that taped his own cord (company policy says that you cannot use a tool that hasn't had a quarterly check). It turned out that the little wrap of colored tape on the cord did nothing to correct the fact that the ground and hot were reversed in the plug. He got a nasty jolt and brought it to me for "repair". He, of course, had no idea how it got reversed or coded.

Top
#149826 - 08/07/04 08:04 AM Re: Power Tool testing?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Big Ed,
 Quote:
Even with a PAT, it only proves that the device was ok when it was checked. 10 minutes later some knot-head can have dropped it in a bucket of water.

Oh how true!.
But with any sort of testing, it only gives you an indication at the time of testing.
So having said that, why do we bother?.
I'll tell you why, because in some places it's required by Law.
Secondly, it is a way to cover your own @$$, no test results will ensure that you are made out to be an idiot in a Court of Law.
Thirdly, Insulation Resistance testing can be handy during Fault-Finding.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#149827 - 08/08/04 10:07 PM Re: Power Tool testing?
Big Jim Offline
Member

Registered: 07/18/03
Posts: 377
Loc: Denver, CO USA
In our facility, before we switched exclusive to double insulated tools, there was a tester on the tool crib counter and every electric tool was hooked to it before it was issued, every time.

Top
#149828 - 08/13/04 05:55 AM Re: Power Tool testing?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Guys,
There is a regime that is looking to step on unsafe Appliances, like Drills, Saws and other such equipment.
But at the end of the day, most of the accidents happen because of poorly maintained Extension leads, getting cut on sharp edges and the like.
We had a worker killed here a few years ago in a new house that had the cord wrapped around the Aluminium ladder, 2 or 3 strands from the phase wire had contacted the ladder, we found him later, I tried to re-susitate him, but to no avail.
This cord was tagged too!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top