The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 208 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#14737 - 09/30/02 09:22 PM lighting contactor
Jimsuper Offline
Junior Member

Registered: 10/01/02
Posts: 3
Loc: Norristown, PA
Just installed a lighting contactor for parking lot lights at 480 volts. I used a 277 volt coil using the line 1 voltage of 277 volts to send thru a photo-cell on the line side. When the photo-cell is activated it would pull in the contactor on the load side, turning the lights on. When testing this after completion by putting the box over the cell to similate darkness, the photo-cell was blown apart after the lights had switched off for approximately 20 - 30 seconds.
One side of the coil was connected to a common as well as the photo cell white wire being connected to the same common. Any ideas as to why it blew apart? Any suggestions for a remedy?
Thank you.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#14738 - 09/30/02 09:29 PM Re: lighting contactor
TE Offline
Member

Registered: 08/26/02
Posts: 37
Loc: USA
My first thought?

Was it a 120v photo-cell?

Top
#14739 - 09/30/02 09:34 PM Re: lighting contactor
Jimsuper Offline
Junior Member

Registered: 10/01/02
Posts: 3
Loc: Norristown, PA
TE

The photo-cell was a 120/277 rated appliance.

Top
#14740 - 10/01/02 04:07 AM Re: lighting contactor
Trainwire Offline
Member

Registered: 03/15/02
Posts: 364
Loc: Strasburg,PA,USA
Just finished a job like that. (see the job comes together thread of a few weeks ago.)Make sure that you are running the other side of your sensor to the neutral line. If it's not your putting 480 across the light cell. Sorry if I'm being elementry but you always double check yourself when the troubleshooting starts.
Next question, where in the scheme of things is the light sensor? Is it in a building where you are pulling the power, or is it mounted to one of the light poles. If you have room for it I think I would recommend a transformer to take your control voltage down to 110 or less. That way the guy behind you changing the sensor doesn't get a rude suprise.
Good luck, troubleshooting is always the fun part.
Trainwire

Top
#14741 - 10/01/02 05:32 AM Re: lighting contactor
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Was the photocell rated for an inductive load?
The fact that the cell was damaged by switching OFF suggests that the collapsing magnetic field may have damaged it.

[This message has been edited by Redsy (edited 10-01-2002).]

Top
#14742 - 10/01/02 07:09 AM Re: lighting contactor
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
Never forget--it's highly desirable to keep molten copper from splattering on you or your clothes.

Hope there is a properly rated fuse in the control circuit. Like, say, a KTK-3R... I would not repower anything without a proper control-citcuit fuse.

It's just a careful process of elimination.

Was it a plugin photocell? Bench test the new photocell.

Trace all wiring. Check voltage with the cell unplugged. Then connect a milliammeter in the line/usually "black" lead of the cell and carefully power it.

It is remotely possible the cell was defective, but make damn sure everything else is OK before the second "test."




[This message has been edited by Bjarney (edited 10-01-2002).]

Top
#14743 - 10/01/02 09:04 AM Re: lighting contactor
Jimsuper Offline
Junior Member

Registered: 10/01/02
Posts: 3
Loc: Norristown, PA
We installed a new Intermatic photo-cell rated for only 277 volts and it held. Apparently, the previous cells were defective. They both blew out at the photo eye itself.