#14703 - 09/29/02 09:04 PM 3 phase amperage
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Just to confirm my thinking, on a 208v 200a 3ph service, (providing the wire is the correct size), is good up to 200amps per phase measured with an amp clamp.
But the total would not be 600 amps, correct?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#14704 - 09/29/02 10:32 PM Re: 3 phase amperage
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
If you have 200A being drawn on each phase, then no, you can't really say that the total is 600A because of the 120-degree phase difference between phases. That same phase difference is the reason why if you have exactly the same current flowing on each phase then the neutral current will be zero.
Top
#14705 - 09/29/02 10:52 PM Re: 3 phase amperage
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
I would say that you are correct, it depends upon the size of your protection on the circuit and the cable size.
You would think that you could directly add the line currents together, unfortunately, this not so, .
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#14706 - 09/30/02 07:07 PM Re: 3 phase amperage
jlhmaint Offline
Member
Registered: 05/25/02
Posts: 202
Loc: Fredericktown, OH, U.S.A
you are correct. 200amps is what you will read on each leg but you don't add them up. It is just 200amps
Top
#14707 - 09/30/02 09:31 PM Re: 3 phase amperage
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
If one of the legs was a 208v to grd wild or high leg, I assume it would still be the 200amp max on each leg, on a 200a service. Also correct?
Thanks for your help,
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#14708 - 10/01/02 03:44 PM Re: 3 phase amperage
arseegee Offline
Member
Registered: 01/28/02
Posts: 324
Loc: Statesboro, GA USA
If your B leg is 208 to ground, you're on a delta secondary and thats actually a 240/120 delta. But youre still a 200A service. You will read 240 between phase to phase.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals