The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#14693 - 09/29/02 04:06 PM Reason for tripped fuses
moe707 Offline
Junior Member

Registered: 09/29/02
Posts: 3
Loc: Bay City, MI, USA
At the shop, we pulled wires from a busway box that is protected with 60 Amp. fuses to wire a single phase 220v machine. The wires were pulled to a 60 Amp disconnect switch box. We also pulled wires to a second circuit breaker panel of the load side (not fuse side) of the machines disconnect box. The second panel will serve the lights, receptacles. The common and the ground of the second panel are run separate to the machine disconnect box. Is this ok?

While wiring a baseboard heater that will be protected by a 30 Amp. breaker in the second box (above) my helper and by mistake connected the in and out on the thermostat with the same hot wire and when we turned on to try the heater, it tripped the breaker which is a good sign that the 30 Amp. breaker worked. My problem is this: Why did the two 60 Amp. fuses at the busduct trip? I am kinda concerned.

Thanks for the help and the directions.
Moe

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#14694 - 09/29/02 07:21 PM Re: Reason for tripped fuses
electric-ed Offline
Member

Registered: 07/08/02
Posts: 184
Loc: Canada
Generally, fuses operate much faster than circuit breakers due to the inertia of the moving contacts.

I am concerned about your question-
"The common and the ground of the second panel are run separate to the machine disconnect box. Is this ok?"

If you mean that the grounded (neutral) and the equipment grounding conductors are in a different conduit than the hot wires, that is definitely not OK.

Ed