#14693 - 09/29/02 04:06 PM Reason for tripped fuses
moe707 Offline
Junior Member
Registered: 09/29/02
Posts: 3
Loc: Bay City, MI, USA
At the shop, we pulled wires from a busway box that is protected with 60 Amp. fuses to wire a single phase 220v machine. The wires were pulled to a 60 Amp disconnect switch box. We also pulled wires to a second circuit breaker panel of the load side (not fuse side) of the machines disconnect box. The second panel will serve the lights, receptacles. The common and the ground of the second panel are run separate to the machine disconnect box. Is this ok?

While wiring a baseboard heater that will be protected by a 30 Amp. breaker in the second box (above) my helper and by mistake connected the in and out on the thermostat with the same hot wire and when we turned on to try the heater, it tripped the breaker which is a good sign that the 30 Amp. breaker worked. My problem is this: Why did the two 60 Amp. fuses at the busduct trip? I am kinda concerned.

Thanks for the help and the directions.
Moe
Top
Work Gear for Electricians and the Trades
#14694 - 09/29/02 07:21 PM Re: Reason for tripped fuses
electric-ed Offline
Member
Registered: 07/08/02
Posts: 175
Loc: Canada
Generally, fuses operate much faster than circuit breakers due to the inertia of the moving contacts.

I am concerned about your question-
"The common and the ground of the second panel are run separate to the machine disconnect box. Is this ok?"

If you mean that the grounded (neutral) and the equipment grounding conductors are in a different conduit than the hot wires, that is definitely not OK.

Ed
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals