#14682 - 09/28/02 10:44 AM Grounding w/o a water pipe
falcondfb Offline
Member
Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
the service is as such:
residential 200A overhead, seu drop to meter pan, pvc nip to nema 3r breaker enc, 4 cond seu to main lug panel in house.
there is a well with plastic piping into house, and since this is my first install where city water piping doesn't exist i'm not sure how to ground the system. I drove 2 g/r w/ the usual #6 but i'm don't think that is enough. Please shed some insite
Top
Work Gear for Electricians and the Trades
#14683 - 09/28/02 11:01 AM Re: Grounding w/o a water pipe
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
You're done!! You must bond the water pipe to the service. If you like, you can catch the water pipe on the way to the ground rods, or run a separate conductor out of the service to catch it.

Suggest - bond around fiberglass collar on ductwork at unit.
Top
#14684 - 09/28/02 12:37 PM Re: Grounding w/o a water pipe
Electra Offline
Member
Registered: 07/29/02
Posts: 38
Loc: Portland, Oregon, USA
Here in Oregon, if this was new construction, a ufer ground would also be required.
Top
#14685 - 09/28/02 12:50 PM Re: Grounding w/o a water pipe
arseegee Offline
Member
Registered: 01/28/02
Posts: 324
Loc: Statesboro, GA USA
Might want to check your GEC w/ 250.66. Think you'll need a #4 copper for the 200A service.

[This message has been edited by arseegee (edited 09-28-2002).]
Top
#14686 - 09/28/02 12:59 PM Re: Grounding w/o a water pipe
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
arseegee,
As long as the GEC is only going to a rod, #6 is the largest that the code requires. See 250.66(A).
Don
_________________________
Don(resqcapt19)
Top
#14687 - 09/28/02 02:29 PM Re: Grounding w/o a water pipe
arseegee Offline
Member
Registered: 01/28/02
Posts: 324
Loc: Statesboro, GA USA
Don, has this changed for 2002, I was taught that if a driven rod is your only GE then you size the GEC from the table. I thought you only used #6 if the rod was a supplemental electrode... guess I'm confused.
Top
#14688 - 09/28/02 03:09 PM Re: Grounding w/o a water pipe
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
arseegee,
No change in the code rule, however in the '96 and earlier codes this rule was Exception #1(a) to 250-94. The rod really isn't a very good electrode and it will never carry very much current into the earth. A #6 is more than enough copper to carry the current that the rod can put into the earth and that is why the rule exists. There is no electrical advantage to installing a larger GEC to the rod.
Don

[This message has been edited by resqcapt19 (edited 09-28-2002).]
_________________________
Don(resqcapt19)
Top
#14689 - 09/29/02 09:14 AM Re: Grounding w/o a water pipe
falcondfb Offline
Member
Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
thanks for the replys, i had all the same thoughts but wasn't sure which way to go. i wish i had gotten a rod under the basement floor
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals