The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#14682 - 09/28/02 10:44 AM Grounding w/o a water pipe
falcondfb Offline
Member

Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
the service is as such:
residential 200A overhead, seu drop to meter pan, pvc nip to nema 3r breaker enc, 4 cond seu to main lug panel in house.
there is a well with plastic piping into house, and since this is my first install where city water piping doesn't exist i'm not sure how to ground the system. I drove 2 g/r w/ the usual #6 but i'm don't think that is enough. Please shed some insite

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#14683 - 09/28/02 11:01 AM Re: Grounding w/o a water pipe
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
You're done!! You must bond the water pipe to the service. If you like, you can catch the water pipe on the way to the ground rods, or run a separate conductor out of the service to catch it.

Suggest - bond around fiberglass collar on ductwork at unit.

Top
#14684 - 09/28/02 12:37 PM Re: Grounding w/o a water pipe
Electra Offline
Member

Registered: 07/29/02
Posts: 38
Loc: Portland, Oregon, USA
Here in Oregon, if this was new construction, a ufer ground would also be required.

Top
#14685 - 09/28/02 12:50 PM Re: Grounding w/o a water pipe
arseegee Offline
Member

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Might want to check your GEC w/ 250.66. Think you'll need a #4 copper for the 200A service.

[This message has been edited by arseegee (edited 09-28-2002).]

Top
#14686 - 09/28/02 12:59 PM Re: Grounding w/o a water pipe
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
arseegee,
As long as the GEC is only going to a rod, #6 is the largest that the code requires. See 250.66(A).
Don
_________________________
Don(resqcapt19)

Top
#14687 - 09/28/02 02:29 PM Re: Grounding w/o a water pipe
arseegee Offline
Member

Registered: 01/28/02
Posts: 321
Loc: Statesboro, GA USA
Don, has this changed for 2002, I was taught that if a driven rod is your only GE then you size the GEC from the table. I thought you only used #6 if the rod was a supplemental electrode... guess I'm confused.

Top
#14688 - 09/28/02 03:09 PM Re: Grounding w/o a water pipe
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
arseegee,
No change in the code rule, however in the '96 and earlier codes this rule was Exception #1(a) to 250-94. The rod really isn't a very good electrode and it will never carry very much current into the earth. A #6 is more than enough copper to carry the current that the rod can put into the earth and that is why the rule exists. There is no electrical advantage to installing a larger GEC to the rod.
Don

[This message has been edited by resqcapt19 (edited 09-28-2002).]
_________________________
Don(resqcapt19)

Top
#14689 - 09/29/02 09:14 AM Re: Grounding w/o a water pipe
falcondfb Offline
Member

Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
thanks for the replys, i had all the same thoughts but wasn't sure which way to go. i wish i had gotten a rod under the basement floor