The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#145404 - 05/13/06 08:25 AM O/Head Fluorescent Light Tube Hight Regs.
Uppeydog Offline
Member

Registered: 07/09/04
Posts: 64
Loc: Loch Lomond
Is there a regulation for wattage/min.height on O/Head fluorescent lighting?

For example, I'm replacing old fittings in a workshop for new. The fittings on the roof will be ok as they are approx. Min.5Mtrs. up, but the fittings above the workbenches are approx.2.8Mtrs. up. All the fittings are: 2x8ft tubes @ 100W/tube.

Thanks,

John U.



[This message has been edited by Uppeydog (edited 05-15-2006).]
_________________________
All I Wanted Was A Cup Of Tea!!

Top
Test Equipment:

Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

#145405 - 05/17/06 11:38 PM Re: O/Head Fluorescent Light Tube Hight Regs.
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
John,
Why not go with some T5 fittings?.
I'm not aware off-hand of anny minimum hieghts, but I do know there are minimum lux levels for most types of work.
Using a T5 system, you can have the fittings a lot higher off the floor.
You also (if used in an industrial situation) have no problems with strobo-scopic effect.
You also have a lower wattage per fitting and therefore, less heat loss, as there is no wire-wound ballast to power as there is only a High Frequency Ballast, no starters to wear out and the tubes last longer.
The best part about these fittings is the fact that they give a higher output (lumens/watt) than any other light source currently on the market.
The T5 tube was designed with a new Tri-phosphor mix in the tubes.(No Mercury either)
These are slowly taking on Metal-Halide lamps for a preferred light source in a lot of applications.
They are so light-wieght (as opposed to the bulk of the M-H control gear) and virtually maintenance-free, it would be a crime to specify anything less.
This is just my own opinion.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#145406 - 05/18/06 04:10 AM Re: O/Head Fluorescent Light Tube Hight Regs.
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
I can't think of anything specific about mounting heights, unless there's something in one of the numerous Health & Safety at Work Acts which would be enforced by H.S.E. in a commercial workshop.

Even so, I can't see fluoros at over 9 ft. above the benches being a problem.

Top
#145407 - 05/26/06 11:42 PM Re: O/Head Fluorescent Light Tube Hight Regs.
uknick Offline
Member

Registered: 02/10/06
Posts: 10
Loc: England
Here in the UK 8ft 125w/100w/85w tubes are being slowly phased out it is now reccommended to use up to 6ft and some stores are using T5 1200MM in banks of 3 with great effect.

Top
#145408 - 05/27/06 01:53 AM Re: O/Head Fluorescent Light Tube Hight Regs.
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Ah! I hadn't realized that there were plans to phase out 8 ft. fluoros, but I've noticed that the range of fittings available in that length seems to have gotten smaller recently.

Top
#145409 - 05/27/06 03:05 AM Re: O/Head Fluorescent Light Tube Hight Regs.
Uppeydog Offline
Member

Registered: 07/09/04
Posts: 64
Loc: Loch Lomond
Thanks for those replies..excellent! These T5 units sound great.

I've allready completed the job, .....but pity I didn't put the question forward before I started!
I didn't know this size fitting was being phased out......SO THAT'S WHY WE GOT THE LOT FOR NOTHING!!!
I collected a couple of pallets full, 30 fittings..all full of rain water as they were left out-side. Stripped them all down,
left them all spread out in the scorching Scottish sun, tested them all.. (I thought I better put that in before you start shouting at me!). Only had to bin one.

So when the foreman starts to annoy me about something, I'll just casually say,"well the lights look great, pity they'll only do for a couple of years!!"

I won't tell him in the next couple of weeks
as lay-offs are looming!!
_________________________
All I Wanted Was A Cup Of Tea!!

Top
#145410 - 05/27/06 12:20 PM Re: O/Head Fluorescent Light Tube Hight Regs.
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Lighting design- at once the most mundane and most exacting part of the trade!

There are sundry references giving you the amount of light you should have in differing areas. There are two problems with these tables, though:
-You never have a way of measuring "foot-candles" ; and,
- You never have the information you need to define the work area properly!

The tables also fail to recognise that, with lighting, quality is even more important that quantity.

Probably the best example I've seen of poor lighting design was a custom kitchen, done entirely with recessed lights. While ther was a tremendous amount of light on the counter-tops, the room had a "cave" feel to it, as there was little light bouncing off the walls.

Likewise, this town has many warehouses lit inside with Sodium HID. While a 'light meter' will tell you there's plenty of light, the yellow light is simply awful for reading lables and doing paperwork. Eyestrain is not a good thing.

As for mounting heigth, this is a design issue.
You want the lights high enough that they don't get hit by goods being moved about.
The downside is that, the higher they are, the more lights are needed to get the desired foot-candles on the workspace. It is also harder to change the bulbs.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals