#14363 - 09/19/02 03:20 PM HVAC marked circuit breakers
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
If a circuit breaker is used as an overcurrent protective device for air conditioning equipment must it be marked "HVAC"?
I've searched Article 240 and could not locate that as a requirement.
I found SWD and HID marked circuit breakers (NEC 240.83(D) but no requirement for HVAC.
Top
Work Gear for Electricians and the Trades
#14364 - 09/19/02 03:42 PM Re: HVAC marked circuit breakers
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Frank:
I can't give articles as my NEC is at the office.
The nameplate that is on the condenser unit, states either FUSE or HACR CB as the required overcurrent protection required for each unit.
We have to follow the mfg instructions, and use the nameplate data.
IF it says "fuses" then the circuit must be protected by fuses. If it says "HACR CB" then a HCAR CB in the panel and a non-fused disco at the unit.
Somebody post the articles please.

The above is stated IMHO, as "Sparky66WV says
John
_________________________
John
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals